question

udo229 avatar image
udo229 asked

current transformer multiplus II

has somebody the multiplus-II successful implemented with the current transformer to optimize self consumption with no feed in into the grid?

There is no documentation whatsoever....

Multiplus-II
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
boekel avatar image
boekel answered ·

The current transducer replaces the internal one so the behavior is exactly the same as if the current would flow through the unit.

I don't know how accurate this is when compared to a real energy meter.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

udo229 avatar image
udo229 answered ·

seems not so accurate...

I think it is an error in the software or the settings

The Multi is always pumping Energy back to the Grid, wich make the Gridmeter rotating backwards...

The Transformer is on the right PHase and in the right direction (mounting it in reverse makes the multi using power from the grid to load the batteries although they are over 80% soc and the PV is delivering 2,5 kw...)

Selecting "no feed in" or "feed in excessive solar charger power" does not alter the behaviour.

I am desperate...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nigelfxs avatar image
nigelfxs answered ·

I have a setup similar to the following diagram, and it works correctly to prevent power feedback to the grid. Are you using the ESS Assistant on the Color Control GX?


ess-dc-pv2.png (169.8 KiB)
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image
boekel answered ·

Can you share / check:


-is Pylontech BMS selected as battery monitor

-what are the parameters sent by the Pylontech BMS (in remote console, devices, pylontech, parameters)

-what are the charge / discharge voltages set in the Multi? (VE Config) and ESS assitant settings? (select the assistant and click 'summary')
-what is the battery voltage

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

apple047 avatar image
apple047 answered ·

Did you manage to make it work? What current transformer have you used? What cable and distance?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

johnsmith avatar image
johnsmith answered ·

Was this a firmware issue in the end?

1 comment
2 |3000