Suitable Circuit breaker between multiplus-ii and battery

Hello everyone,

I want to put a double pole MCB between a MultiPlus-II 48/3000/35-32 and 3 48V Pylontech batteries.

Pylontech recommends 25A for each Package and it supports up to 100A of discharge for each Package.


Victron states in manual:


-You must have the minimum number of battery modules to supply the inverters startup inrush surge currents that charge the capacitors when the inverter is first connected, this occurs prior to any loads being connected. For this Inverter, 2 Batteries are minimum.

-Victron recommends a 125A MCB between battery and Inverter, since its Peak power is 5500Watt (3000 AC Load + 1500 feeding in shore power)

We dont want to feed in the shore power, so only ac loads left. 3000 W / 48 V = 62,5 A. So an 80A MCB should be fine, but maybe the Inverter wants to pull more current? Maybe the stated 125A due to the startup inrush current?


I found 3 MCBs (80A, 100A, 125A) from the same series from ABB

https://new.abb.com/products/2CCF019606R0001/s802pv-sp80-high-performance-mcb


I really would like to use an 80Amp MCB, so that the Inverter does not pull much more than the calculated 62,5 Amps.


My Questions:

Do you think the 80Amp MCB will "handle" the startup inrush current?

Does the MCB could have a minimum operating Voltage(Datasheet not found)? Is 48V fine?

Is the rated Ultimate Short-Circuit Breaking Capacity (Icu):(800 V DC) 5 kA enough for a 7,2kWh battery system?

If you have remommendations for other MCBs, please share.

Multiplus-IIMultiPlus Quattro Inverter ChargerPylontechbattery
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bjorn-n avatar image bjorn-n commented ·

You are mixing all kinds of concepts that shouldn't be mixed. Looking at the types of questions you ask, I recommend you hire a professional. Or, before you do it yourself, you read up a lot on basic concepts such as voltage, current, power. For your own safety.

If you are on a boat, I recommend you also read up on galvanic isolation. As not taking that into account could mean that a couple of years from now, the hull of your boat is... Well ready for the scrap yard.

1 Like 1 ·
alan avatar image alan commented ·

The peak power has nothing to do with the AC feed in, it's the surge capacity of the Inverter.
It can deliver 5500w for 0.5s. This is why the 125A fuse.

The ac feed in flows through the AC bus and can only supply the inverters max charge spec (model dependant) to the DC bus. 35A in this case.

0 Likes 0 ·
Cansin Sari avatar image Cansin Sari alan commented ·

Hey alan,

god bless you. I was searching the whole web for those 5500 Watt of the Inverter. Does it also mean, that the Inverter can pull 5500Watts from the Batteries in an offshore case ?

Is this product suitable for our application?

https://new.abb.com/products/de/2CCF019608R0001/strangsicherung-s802pv-sp125-800v-dc-125a-2-polig

Is the rated Ultimate Short-Circuit Breaking Capacity of 5 kA enough for our system or should we choose a higher one more like 15kA?

Please reply quickly

Cansin



0 Likes 0 ·
5 Answers
seb71 avatar image
seb71 answered ·

Better use a fuse (not an MCB) for any wire connected to the battery.

For for the battery-busbar positive wire I use a HRC fuse in a base like this:

kvl-00.jpg


kvl-00.jpg (760.5 KiB)
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Cansin Sari avatar image Cansin Sari commented ·

Why a fuse

0 Likes 0 ·
seb71 avatar image seb71 Cansin Sari commented ·

It is safer.

0 Likes 0 ·
rslifkin avatar image rslifkin seb71 commented ·

How is a fuse safer? If it's got an appropriate trip curve, adequate interrupt rating, etc. then it shouldn't matter if it's a fuse or a breaker.

0 Likes 0 ·
seb71 avatar image seb71 rslifkin commented ·

It is more reliable than an MCB. Especially for DC.

0 Likes 0 ·
nigelfxs avatar image nigelfxs Cansin Sari commented ·

Another reason is that you cannot use a regular AC Circuit Breaker on a DC battery circuit - it can easily catch fire! See AC Circuit Breaker 230V DC Test

A DC fuse and holder is also a lot cheaper than a similarly rated DC Circuit Breaker.

[Edit] I see that the ABB breakers in your first post are DC-rated, so will work. They are probably quite expensive.

0 Likes 0 ·
geko22 avatar image geko22 nigelfxs commented ·

V.errückterweise sind die Sicherungen bis 60 VDC zulässig, so mal eine Info. Ich würde jedoch auf das Typenschild achten.

0 Likes 0 ·
alan avatar image
alan answered ·

Something along these lines is what you are looking for if you want to go the breaker route.

https://www.outbackmarine.com.au/noark-125a-500v-dc-circuit-breaker-2-pole

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Cansin Sari avatar image Cansin Sari commented ·

Hey alan,


god bless you. I was searching the whole web for those 5500 Watt of the Inverter. Does it also mean, that the Inverter can pull 5500Watts from the Batteries in an offshore case ?


Is this product suitable for our application?


https://new.abb.com/products/de/2CCF019608R0001/strangsicherung-s802pv-sp125-800v-dc-125a-2-polig


Is the rated Ultimate Short-Circuit Breaking Capacity of 5 kA enough for our system or should we choose a higher one more like 15kA?



Cansin

0 Likes 0 ·
alan avatar image alan Cansin Sari commented ·

Yes, the inverter can supply 5500w from the batteries for 0.5s in any configuration. More details here. But don’t buy an inverter and depend on its overload capabilities to run a load.

https://vimeo.com/378902603


Maximum input through the AC bus in 32A, so 7360, which when combined with the output of 5500w from the inverter makes 12860w. But this is on the AC side only.

The DC bus, can charge at 35A (1680w) or draw at ~115A (5500w surge).


The breaker I linked to has a 25kva breaking capacity.

You need to do some of your own research. I’m a big fan of teaching a man to fish so to speak.

https://en.m.wikipedia.org/wiki/Breaking_capacity

http://en.pylontech.com.cn/products.aspx?id=48


Feel free to ask if the answer you conclude is ok.

0 Likes 0 ·
Cansin Sari avatar image Cansin Sari alan commented ·

Hey Alan,

I contacted the battery manufacturer Pylontech and asked them for the details of the US2000 battery.

The US2000 battery can have a voltage of 55V at an internal impedance of 20mΩ.


Quick Calculations for 3 US2000 batteries in a row:

55V/20mΩ = 2750A

2750A * 3= 8250A

So the breaking capacity should be higher than 9kA.

Since my battery has the highest capacity, I made the breaking capacity calcuations according to the technical characteristics of the battery.

Please see also my schematich https://community.victronenergy.com/questions/80567/camper-van-schematic-please-critique.html#

Do you agree ?



0 Likes 0 ·
alan avatar image alan Cansin Sari commented ·

The pylontech data sheet states 100A for 15 sec. So 55v x 100A = 5500w x 3 = 16500w

so 16.5kw


VA is essentially watts.


The BMS will shutdown with this load after 15 sec, however you want the breaker to be able to break during this discharge.

0 Likes 0 ·
bjorn-n avatar image
bjorn-n answered ·
-Victron recommends a 125A MCB between battery and Inverter, since 
its Peak power is 5500Watt (3000 AC Load + 1500 feeding in shore power)

Hold your horses! First remark, you are adding power between battery-inverter (DC side) and from the inverter-grid (AC-side). Second, fuses and breakers don't care so much about power. They care about current. Oh and fuses also care about if it's alternating current (AC) or direct current (DC). So you can't just add up the DC side and AC side of things. That's just... wrong :-)

DC side

The peak supply current between the battery and the inverter is 35A. So in normal circumstances the wires between the battery and the inverter would get 35A at most. Depending on the voltage of your battery that would be roundabout 48V*35A=1680VA=1680W. But as I said, your fuse/breaker doesn't care about power.

For your information, I happen to have a 160A fuse on the DC side of things. After playing a lot with it, I have now a better understanding of how the device works. In hindsight, it would have been better to have a 40A fuse in stead. But then again, maybe those fuses would blow when the capacitors are charged (when you first connect a battery to the MultiPlus). This can be easily solved by not using fuses at that point in time, leave it connected for a second and then put the 40A fuse in between. But I digress.

Could you use a MCB in stead of fuse. Sure, as long as it's an MCB desigend and built for DC. Which are like at least 10 times the price of a fuse. How often do you intend to trip the breaker? In my case: my goal is zero times. So I'm cheaper of with a fuse (and a few spare ones). Furthermore, I can cheaply increase/decrease the current at which the fuse goes by replacing it.

AC side

The peak supply current between the device and the grid is 32A. So a (regular) AC breaker of 32A would be fine. Although I would consider going one step beyond to 40A depending on your actual use. Now the maximum power that can flow through the AC side of the device is 32A*230V=7360VA. Let's make a simplification by assuming the power factor is 1 so that's equivalent to 7360W.

Since it's AC on this side, you can use a (commonly available) AC MCB of 32A or 40A.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bjorn-n avatar image bjorn-n commented ·

I stand corrected about the 40A fuse on the DC side. I have been running some more tests. Although the battery charger outputs 35A at most, the inverter can output more current (around 45-47A).

So a 40A fuse on the DC would melt in such a case. You need a fuse that can resist a higher current (e.g. 135A like Victron Energy recommends for the MultiPlus-II 48/3000/35-32).

screenshot-at-2021-05-14-17-57-50.png

0 Likes 0 ·
zoneblue avatar image
zoneblue answered ·

I have blown up a couple of Noarc products using inverters on Lithium. So far never killed the black Carling DC rated breakers. Kinda large, but kinda cool.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

zeron avatar image
zeron answered ·

I'm using a Schneider Electric A9N18459 125A MCB between my Multiplus-II 5000 and 4 Pylontech batteries, it's rated up to 250 VDC (and quite expensive...)

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

londonflatthing avatar image londonflatthing commented ·
are you using just a single pole (on positive) or double pole?
0 Likes 0 ·