question

udo229 avatar image
udo229 asked

current transformer multiplus II

has somebody the multiplus-II successful implemented with the current transformer to optimize self consumption with no feed in into the grid?

There is no documentation whatsoever....

Multiplus-II
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

udo229 avatar image udo229 boekel ♦ commented ·

I‘ve just read again the German manual from the victron w3bsite for the multiplus-ll 48 3000 32. I have found one mentioning of the transformer, but nothing about mounting, configuration, behavior, cabling. There is one sentence which says that there is an optional current sensor. That’s all. Nothing else. On the whole victron webspace there is no text about the current sensor.

In the ve configure 3 there is the checkbox „external current sensor (see manual)“

But there is no manual .....

1 Like 1 ·
boekel avatar image boekel ♦ udo229 commented ·

@Guy Stewart (Victron Energy Staff)
Is there more documentation about this? I thought it just replaces the internal sensor as soon as you plug it in...
cable length should also be in the manual.

0 Likes 0 ·
udo229 avatar image udo229 boekel ♦ commented ·

I haven‘t found anything about details of the transformer and its use in any manual.... would be glad for every hint....

0 Likes 0 ·
6 Answers
boekel avatar image
boekel answered ·

The current transducer replaces the internal one so the behavior is exactly the same as if the current would flow through the unit.

I don't know how accurate this is when compared to a real energy meter.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

udo229 avatar image udo229 commented ·

seems not so accurate...

I think it is an error in the software or the settings

The Multi is always pumping Energy back to the Grid, wich make the Gridmeter rotating backwards...

The Transformer is on the right PHase and in the right direction (mounting it in reverse makes the multi using power from the grid to load the batteries although they are over 80% soc and the PV is delivering 2,5 kw...)

Selecting "no feed in" or "feed in excessive solar charger power" does not alter the behaviour.

I am desperate..

0 Likes 0 ·
Show more comments
udo229 avatar image
udo229 answered ·

seems not so accurate...

I think it is an error in the software or the settings

The Multi is always pumping Energy back to the Grid, wich make the Gridmeter rotating backwards...

The Transformer is on the right PHase and in the right direction (mounting it in reverse makes the multi using power from the grid to load the batteries although they are over 80% soc and the PV is delivering 2,5 kw...)

Selecting "no feed in" or "feed in excessive solar charger power" does not alter the behaviour.

I am desperate...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nigelfxs avatar image
nigelfxs answered ·

I have a setup similar to the following diagram, and it works correctly to prevent power feedback to the grid. Are you using the ESS Assistant on the Color Control GX?


ess-dc-pv2.png (169.8 KiB)
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

udo229 avatar image udo229 commented ·

Hello Nigel!

My setup is the same, instead of the Color control GX I use an Octo GX and two MPPT 150/35 and pylontechs. But I think thats marginal. I've installed the ESS Assistant on the Multiplus, so it is shown on the Octo Remote Console.

I've tried a lot, but the Multiplus always starting to feed power into the Grid via AC In.
The current Sensor is placed as shown in Your setup, when I install it 180° reversed (the Arrows showing in direction of the loads), The Multi is pumping energy into the Pylontechs.

Tried a lot of Settings, found a new Firmware today (2628459) today, it looks diefferent in Details on the VE.Config, but always the Multi is pumping power into the grid...

Would be nice to compare your setup and settings!!!!

0 Likes 0 ·
1555522433327.png (32.8 KiB)
nigelfxs avatar image nigelfxs udo229 commented ·

Hi Udo229

I think the important ESS settings, for your issue, are as follows:

  • ESS Mode = Optimized (with BatteryLife)
  • Grid meter installed = OFF
  • Feed-in excess solarcharger power = OFF
  • Grid setpoint = low value (I have set mine to 20W)


0 Likes 0 ·
udo229 avatar image udo229 nigelfxs commented ·

Hello Nigel!

Thanks for your Reply!

I think I tested those settings.

The Actual are like this:

Tomorrow (its night now in europe) I'll try your proposals, but I think I have yet...

Maybe you can download your configuration file via vrm and load it up here?

Then I can open it via VE Configure3 and can try to find a clue in the settings...

Thanks,


Udo

0 Likes 0 ·
1555530225135.png (41.2 KiB)
1555530289312.png (29.1 KiB)
nigelfxs avatar image nigelfxs udo229 commented ·

Hi Udo229

Are you sure that the current sensor is correctly clamped around the Live wire of AC_IN? It must not clamp around more than one wire, and the clamp must "click" closed so that the smooth ferrite surfaces are together.


0 Likes 0 ·
udo229 avatar image udo229 nigelfxs commented ·

Yes, it‘s clamped around the phase wire coming from the main switch leading to the distribution box. I‘ve been working with electronics and electrotechnical installations for 35 years now. It doesn‘t help against all mistakes, but some.

I‘ve drawn a signal from the transformer via an oscilloscope and measured an dc-resistance of approx. 100ohms trough the transformer.

I‘ve given up the idea of measuring the current to/from the grid via the undocumented transformer solution and I hope my grid-meter will arrive next week. RS-485 should work over 20 meters.....

0 Likes 0 ·
henry99 avatar image henry99 commented ·
Do you use only the current transformer and not the EM 24 Energymeter?
0 Likes 0 ·
boekel avatar image
boekel answered ·

Can you share / check:


-is Pylontech BMS selected as battery monitor

-what are the parameters sent by the Pylontech BMS (in remote console, devices, pylontech, parameters)

-what are the charge / discharge voltages set in the Multi? (VE Config) and ESS assitant settings? (select the assistant and click 'summary')
-what is the battery voltage

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

udo229 avatar image udo229 commented ·

udo229_inst_ttyO5_Interfaces_Mk2_Tunnel(4).jpg

here's my Multi-configuration. It's not a jpg, you have to change the ending in ".rvsc" , the upload refuses "rsvc".....

The settings for the pylontech I've found and copied from the Victron Homepage

Here the settings of the batterie in the console:

0 Likes 0 ·
apple047 avatar image
apple047 answered ·

Did you manage to make it work? What current transformer have you used? What cable and distance?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

johnsmith avatar image
johnsmith answered ·

Was this a firmware issue in the end?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pfloryann avatar image pfloryann commented ·

NO..i have 2 multiplus II in parallel and i set the grid setpoint between 110-220w(alternate with node red) to avoid feed in. Now i have feed in 0.1kw per day. I dont want this value for the setpoint but I did not find another solution. Too bad because victron doesn't find a solution for multiplus to respond faster when feed in appears.

0 Likes 0 ·