question

danepb avatar image
danepb asked

Correct AC out 1 Circuit breake size

Good day all,

I am experiencing a dispute on the correct CB size for the AC out 1 of a Multi 3KVA that is operating as a UPS.


Can you please advise.

Regards

Dane

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
JohnC avatar image
JohnC answered ·

Hi @DanePB

The 'correct' size is for your wires to say. But Victron do actually provide breakers for your identical Multi spec within their Easysolar boxes. https://www.victronenergy.com/upload/documents/Datasheet-EasySolar-with-Color-Control-EN.pdf Note 230V ac.

63A main, split to 2x 10A and 2x 16A on ac1, and separate 16A for ac2.

Hard to be more definitive than what Victron push out to their customers themselves.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

danepb avatar image
danepb answered ·

Thank you, i see your point, basically 63A in and 63A out or a 1 to 1


The dispute is on the maximum allowed, in the manual it states, 32A to the Victron 3kva and 45A on AC out 1 ,(13A from the unit and 32A as past through), hence the max is 45A and recommended will be lower.


The distributor is stating the max allowed is 10A in ups mode.


I appreciate any input into this


Regards


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image JohnC ♦ commented ·

All I can think of is that he's setting a limit on what the batts can discharge when the ups is called upon.

0 Likes 0 ·
danepb avatar image
danepb answered ·

I understand that. Does it make the use of a 32A wrong.


He states that you must use the 10A to protect the Victron and that 32A is to much while they unit is online as a back up.

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image JohnC ♦ commented ·

The Multi can look after itself, it doesn't need external protection. It's specs are quite clear about when it will derate or how long it can handle abnormal loads. It will just trip itself if pushed too hard, and won't hurt it.

0 Likes 0 ·
danepb avatar image danepb JohnC ♦ commented ·

Thank you,

That is what I told him. They are stating that because I did not use a 10A breaker, this caused a unit to fail.

The units mosfets poped under charging. They don't want to issue the RMA to Victron.



0 Likes 0 ·
JohnC avatar image JohnC ♦ danepb commented ·

Under charging? Are you perchance using ac-coupled pv on ac-out?

Shouldn't matter anyway. And I've no idea why they wouldn't raise an rma. This isn't the place to discuss it, and we've no feeling for your relationship/situation, but this could be raised to a higher level in the Victron hierarchy if you choose. Just ask if you need leads.

Depends too if it's at your cost. Something fishy here.

0 Likes 0 ·
danepb avatar image danepb JohnC ♦ commented ·

I do, do AC coupled systems, but this one was a strandard backup installation charging from the grid.

I do have the email addresses of the High ups in Victron, I am willing to give the distributor a chance on this. If not, I will go higher. Thank you for your inputs.

Is there a platform where I can get someone higher in victron to discuss this with me?

0 Likes 0 ·
Show more comments
Warwick Bruce Chapman avatar image Warwick Bruce Chapman danepb commented ·

What model and rev on the unit?

I saw a 2629 rev 9 with popped mosfets.

0 Likes 0 ·
danepb avatar image danepb Warwick Bruce Chapman commented ·

2629 not sure on the rev


0 Likes 0 ·