I am experiencing a dispute on the correct CB size for the AC out 1 of a Multi 3KVA that is operating as a UPS.
Can you please advise.
Regards
Dane
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Good day all,
I am experiencing a dispute on the correct CB size for the AC out 1 of a Multi 3KVA that is operating as a UPS.
Can you please advise.
Regards
Dane
Hi @DanePB
The 'correct' size is for your wires to say. But Victron do actually provide breakers for your identical Multi spec within their Easysolar boxes. https://www.victronenergy.com/upload/documents/Datasheet-EasySolar-with-Color-Control-EN.pdf Note 230V ac.
63A main, split to 2x 10A and 2x 16A on ac1, and separate 16A for ac2.
Hard to be more definitive than what Victron push out to their customers themselves.
Thank you, i see your point, basically 63A in and 63A out or a 1 to 1
The dispute is on the maximum allowed, in the manual it states, 32A to the Victron 3kva and 45A on AC out 1 ,(13A from the unit and 32A as past through), hence the max is 45A and recommended will be lower.
The distributor is stating the max allowed is 10A in ups mode.
I appreciate any input into this
Regards
I understand that. Does it make the use of a 32A wrong.
He states that you must use the 10A to protect the Victron and that 32A is to much while they unit is online as a back up.
The Multi can look after itself, it doesn't need external protection. It's specs are quite clear about when it will derate or how long it can handle abnormal loads. It will just trip itself if pushed too hard, and won't hurt it.