question

fanda-eu avatar image
fanda-eu asked

Victron Quattro 8000 is raising frequency to 51Hz when the AC load exceeds 6000W. Off grid mode

I have a Quattro 8000 with

BYD B-Box LV 14kWh battery and the

Sunnyboy 5000 solar inverter

Also using GX console


The systems work great, until the load on the Quattro exceeds 6000W. When that happens the Quattro suddenly increases the frequency to 51Hz, shutting down the solar inverter, which sometimes leads to the overload if the solar inverter was producing power


The ESS and the GSX are upgraded to the latest version. The BYD is not limiting the charge or discharge current when this happens


This behavior also happens at night

MultiPlus Quattro Inverter Chargerfrequency
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fanda-eu avatar image fanda-eu commented ·

Also: Lowering the load to below 6000kW immediately resets the frequency back to 50Hz

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·

Please share your VE.config settings and maybe add some screenshots from the remote console or VRM dashboard.

0 Likes 0 ·
Show more comments
1 Answer
chrigu avatar image
chrigu answered ·

I think you mean 6kW or 6000W load

Wheres the PV-inverter connected to, ACout?

Raising frequency dounds like the Quattro is trying to lower the PV-Inverters output. But it also happens at night?

6kW is close to the Quattros limit. An 8000 unit is able to deliver 8kVA or 6.4kW, with higher ambient temp theres a derate, at 40°C its down to 5.5kW

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fanda-eu avatar image fanda-eu commented ·

Thank you for the reply. You are correct of course, it is 6000W (already fixed)

The PV inverter is connected to the AC out. The frequency raise happens any time the loads goes above 6000W, regardless of the time of the day or the current PV production.

It is like, if the ESS assistant were hardwired to reduce the PV production to minimum (51Hz corresponds to the minimum production on my system) whenever the load exceeds 6000W

0 Likes 0 ·