EV charger and PV inverter question

Hi,

I have following Victron connection :

actual-victron.png

and I want implement a EV charger according this schematics :

ev-charger-victron.png

Question is, what is benefit / disadvantage of the connection on the ACin / ACout of the Multiplus.

Second question is, which PV inverter to use. Is there any compatibility list ? I know, that Fronius is supported, but is there any other ?

Thank you

Alex

ev charger
actual-victron.png (118.8 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi, I don't see a meter on AC IN, that's mandatory for automatic mode

0 Likes 0 ·
4 Answers
daza avatar image
daza answered ·

AC PV wise you are not limited but you have the fronius and another the name escapes me that integrates with victron software wise, but you can have any other AC PV as long as you use an energy meter ET112 and similar with units that don’t integrate at base level with victron

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alda avatar image
alda answered ·

I have a ET340.

Is better connect AC PV on the ACin or ACout of the Multiplus ?


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image
daza answered ·

Depends what you want to do with the solar ie surplus to charge the EV after the multi then Ac out is best other wise you would use some of the multis head room by pushing the solar through the AC In by the way that monitor will be fine. If you want PV in a grid down situation then AC out is where you want it, if you would rather export a a lot or all of your solar I would go AC in, instead of pushing it through the multi, the system is very versatile and you can do it as you see fit

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alda avatar image
alda answered ·

My priority is EV and use as much as possible for my usage. Export isn't important.

So it looks like a ACout is the best place for it.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

You can use it on both sides, it's the same. The advantage on ac in - you are not limited by the power of the inverters but if the grid fails, EVCS stops, and the opposite on ac out.

0 Likes 0 ·