Solar charger sizing query.

The voc of my 3 x 245w panels is 159v, would I be right in thinking i can connect my panels in parallel and use a 150/70 charge controller? I'm running a 12v system.

Thanks in advance.

charge current limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
Murray van Graan avatar image
Murray van Graan answered ·

Please clarify, Is it 159Voc per panel or all three in series?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

frosty avatar image
frosty answered ·

159v voc would be all three connected in series.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Justin Cook avatar image
Justin Cook answered ·

Negative; the 150v input rating is a HARD LIMIT and must not be exceeded under any circumstances. You could, however, wire two in series and keep the third in parallel and -depending on the other specs of your panels- be fine.

12 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

frosty avatar image frosty commented ·

I realise the voltage shouldn't be exceeded, I was under the impression that if I connected all three panels in parallel that I'd be well under the limit and able to use a smaller less expensive controller, the 150/70.

0 Likes 0 ·
frosty avatar image frosty frosty commented ·

Have I missed something?

0 Likes 0 ·
Show more comments
klim8skeptic avatar image klim8skeptic ♦ frosty commented ·

Panasnic hit's?

3 parallel on a 100/50 will be ok for a 12v battery system. You will need string fuses though.

0 Likes 0 ·
Show more comments
kevp avatar image kevp commented ·

Justin, Can you explain a little more about 2S 1P config. I did not realise that was possible, it may open up module upgrade for my current MPPT. Are there any drawbacks?

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ kevp commented ·

A diagram from Wiring Unlimited.


0 Likes 0 ·
solar-array.jpg (90.2 KiB)
Nickus de Vos avatar image Nickus de Vos kevp commented ·

I would also like to know, from what I heard if you have 3 panels, you should never connect 2P 1S or 2S 1P and that S and P strings should always be equal numbers like 4 panels 2P 2S or 6 panels 3P 2S etc.

0 Likes 0 ·
JohnC avatar image
JohnC answered ·

Hi Frosty. Agree that paralleled into 12V batts would be fine.

Just adding that you wouldn't need a 150/ mppt in that case, and I'd actually suggest you consider a 100/50, which would rarely (if ever) clip at the A-limit into typical charge voltages. Might save you some coin..

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

frosty avatar image
frosty answered ·

I wondered if that would be the case, appreciate the reply, cheers.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic