question

frosty avatar image
frosty asked

Solar charger sizing query.

The voc of my 3 x 245w panels is 159v, would I be right in thinking i can connect my panels in parallel and use a 150/70 charge controller? I'm running a 12v system.

Thanks in advance.

charge current limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
Murray van Graan avatar image
Murray van Graan answered ·

Please clarify, Is it 159Voc per panel or all three in series?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

frosty avatar image
frosty answered ·

159v voc would be all three connected in series.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Justin Cook avatar image
Justin Cook answered ·

Negative; the 150v input rating is a HARD LIMIT and must not be exceeded under any circumstances. You could, however, wire two in series and keep the third in parallel and -depending on the other specs of your panels- be fine.

12 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

frosty avatar image frosty commented ·

I realise the voltage shouldn't be exceeded, I was under the impression that if I connected all three panels in parallel that I'd be well under the limit and able to use a smaller less expensive controller, the 150/70.

0 Likes 0 ·
Show more comments
kevp avatar image kevp commented ·

Justin, Can you explain a little more about 2S 1P config. I did not realise that was possible, it may open up module upgrade for my current MPPT. Are there any drawbacks?

0 Likes 0 ·
Show more comments
JohnC avatar image
JohnC answered ·

Hi Frosty. Agree that paralleled into 12V batts would be fine.

Just adding that you wouldn't need a 150/ mppt in that case, and I'd actually suggest you consider a 100/50, which would rarely (if ever) clip at the A-limit into typical charge voltages. Might save you some coin..

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

frosty avatar image
frosty answered ·

I wondered if that would be the case, appreciate the reply, cheers.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic