question

silverstran avatar image
silverstran asked

i installed 8kw 48v quatton victron for my client, the problem is that the bulk light will be blinking and the charging wil pause. can some one help me with a solution


charge current limit
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Kristof G. avatar image
Kristof G. answered ·

I agree with paul b... but maybe this is the answer:


"


MultiPlus is in Bulk-protection mode: the maximum bulk charging time of 10 hours is exceeded. Such a long charging time could indicate a system error (e.g. a battery cell short-circuit).

Solution:Check your batteries and switch the Multi off and back on to restart it.

How to disable bulk protection
The factory setting of the Bulk-protection mode is on. The Bulk-protection can be disabled with VEConfigure.


"

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic