Mixing 15 cell with 16cell banks


struggling with a 15 cell bank (pylontech) and a 16 cell with a pacebms. I have 80kW with the Pace (8 x 200 amp hour) and 37kW with pylontech (11 x us3500c); what happens for me is: when both are connected, only the pace discharges unless the load is extreme (like 10kW, then the pylontech will take a very small % of the load, maybe 5%), If i turn the Pace off and allow the Pylon to discharge as its the only bank, when i turn the pace back on, it dumps whatever it has into the pylon to take that back to 100%. the batteries are connected as follows: 6 pylon, 4 pace to a lynx power in, 5 pylong 4 pace to a second lynx power in, then a lynx shunt , then a lynx distributor which has 3 inverters (voltronic 11kW) the shunt is the aggregator for the battery stats, with the pace connected via can to a cerbo and the pylontech connected to solar assistant for data, i also use SA to monitor the inverters. any insight appreciated.

Show less



Lithium BatteryPylontechlynx shunt16s
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

As you see that doesn't work and is absolutely not recommended.

The 16s battery has a higher voltage level and because of that will always be used first.
The more dangerous thing is you will overcharge the Pylontech!

I guess the 16s battery is DIY? If yes just remove one cell and it should work.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jwnesbitt avatar image jwnesbitt commented ·
its not a DIY, but i guess i could remove 8 cells from the 8 batteries, then buy 7 more cells, giving me an extra battery, ill investigate this some more
0 Likes 0 ·
kevgermany avatar image
kevgermany answered ·

15S means 15 cells in series inside the batteries. 16S means 16.

Pylontechs run at a lower voltage than Pace. So you have two different voltages connected together. Hence the heavy charge transfer.

Although both may be marketed as 48V, it's a nominal figure.

Bottom line is these batteries are not compatible. The BMSs are saving you from a major meltdown. You should rectify this asap. If not done the consequences could be catastrophic. Suggest you get expert advice on how to rectify.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jwnesbitt avatar image jwnesbitt commented ·
thank you, thats what i thought would be the response

when i saw the issue, what i did was turn the Pylontech off, so at the moment, im manually switching between packs, so they are never both on at the same time, this gives me around 5 days usage with little sun (Northern Ireland - so weather is generally grim)

0 Likes 0 ·
the-doon avatar image
the-doon answered ·

Interested to know why you have mixed the 2 different types of battery? What charge settings are you using?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jwnesbitt avatar image jwnesbitt commented ·
i originally bought the Pylontechs, and decided that i wanted to try go completely off grid, so added the 80kW pack. im using the Pylontech parameters for the charging profiles on both batteries
0 Likes 0 ·

Related Resources

Additional resources still need to be added for this topic

Battery Compatibility

Did You Know - How to create a battery profile for non-Victron batteries?

Victron Pylontech battery compatibility guide

Additional resources still need to be added for this topic

Lynx Shunt VE Can online manual


Additional resources still need to be added for this topic