question

goose avatar image
goose asked

Quattro 48/8000 stays in absorption with Pylontech US3000

Good day,

I just want to make sure if this is normal or not...


I have set up everything to the dot from the steps here:

https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom


But what I see is after 48 hours with constant AC-in, the Quattro still stays absorption:

I never saw that it went to float, only see it in absorption...

  • Quattro is newest firmware
  • Venus GX is newest firmware


Is this normal?

Thanks!

battery chargingLithium BatteryPylontechVenus GX - VGX
1584386366779.png (23.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Goose

See faq Q7:

https://www.victronenergy.com/live/ess:design-installation-manual#faq


While discharging, and connected to the grid, the state can still show a charge state, such as Bulk, Absorption or Float. Even though it is not charging. This is normal, nothing to worry about.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

goose avatar image goose commented ·

Thank you for this, but I currently do not have ESS configured, only DVCC for Grid Backup.

Does the same argument apply?

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ goose commented ·

Ah sorry.

The CANbus battery dictates the charge algorithm, so the same applies, it's just charging to the voltage the battery wants it to.

0 Likes 0 ·
goose avatar image goose Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

Thank you very much!

0 Likes 0 ·