bonjour , je me pose une question pourquoi a 1h20 du matin j'ai une alarme error 29 de mon mppt !!! pas compris !
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
bonjour
surement un probleme de réglage entre votre mppt et un autre système de charge:
This error will auto-reset once the battery voltage drops below the float voltage. To protect the battery from over-charging the battery is disconnected.
Possible causes:
over-sized PV array configuration, if there are too many panels in series the battery voltage cannot be reduced any further. Consider wiring more PV panels in parallel to reduce the voltage.
configuration issue, check if the battery settings match with the installation (especially absorption and float voltage settings).
another charger in the system raises the battery voltage above the expected level.
encore une fois, vérifier vos parametrages ...
bonjour encore une fois de plus erreur 29 sur le tableau victronconnecte de mon application !!! erreur 29 toutes les reglage a etait controler 10000 fois et toujours quand la batterie et arrive a 100% DE TEMPS EN TEMPS ERREUR 29 mais pare contre ce qui est bizar regarder le la photos des valeur enregistre sur mppt vebus ou bms aucun voltage superieur 55,.3v rien de rien qui montre un over charge protection la seul infos ce trouve affiche sur application victronconecte sur le mobile !! sur mppt !!! pas le portail vrm que pense M CORTASSA !!!