question

nick5000 avatar image
nick5000 asked

What happened to this cable?

Voltage is 52V at the batteires but only 38V at the Victron Multi input. The 35mm2 cable should be big enough but it's old, maybe corroded (?), could that cause this?photo-2023-12-06-145346.jpeg

Multi RS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

9 Answers
ian0 avatar image
ian0 answered ·

I'd say it overheated due to a bad connection in to the rotary switch.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

regman54 avatar image
regman54 answered ·

Hard to tell by simply looking at a photo but it appears there might have been a sharp kink made in the cable or pinched somehow possibly breaking several strands causing the wire to get very hot at that point and melting the jacket. Don't know for sure but just a guess on my part.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
Lug stacking (shudders). Use a bus bar.
3 Likes 3 ·
Craig Chamberlain avatar image Craig Chamberlain commented ·
If the cable was bent AFTER it was crimped then it can cause the strands to be pulled out of the crimp. This happens due to the difference in length of the strands on the inside of the bend compared to the outside. Always best to shape the cable before cutting the end flush and then stripping and crimping. Not saying that wasn't done here but might be a factor.
3 Likes 3 ·
nesswill avatar image nesswill Craig Chamberlain commented ·

Yes, completely agree I have seen a lot of this in my servicing life.

But also suspect this cable might have been (fatigue) bent a few times in the area of damage causing work hardening, happens in wires just as it does in metal strips, this in turn will cause a higher resistance causing a heat build-up in that area.

1 Like 1 ·
kevgermany avatar image
kevgermany answered ·

It's a fire risk. Replace asap.

It's not clear what the the other black wires are, but a big stack inside the switch may have resistance issues. Better to use a busbar.

If you regularly use the rotary switch, especially under load, you may have damaged the contacts through arcing. Best to check its resistance and replace if necessary.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@Ian0 and @regman54 and. @kevgermany definitely have valid points.

The black underneath should be the second insulation level. If it isn't then that corrosion is really bad and then the cable is wrong.for the application.

Several things to note.

Cable was hot very (obviously). But should have been able to handle the heat if it was an up to standard cable. Causes of heat - bad torque, poor crimp (under crimped) or over crimp so the cable actually became smaller than the recommended 35mm².

The other cause is not using fine strand wire. (Standards again)

If it split there, it could have been damaged insulation damaged during handling and install. Or the cable is not actually up to specifications especially the heat rating (which is very likely the insulation should handle 100s of degrees before smoke) and use of actual copper.

If the corrosion is that bad, then it probably started as a compromised/poorly stored cable. Which means it should not have been installed in the first place. The other thing I have seen on cheaper cable is it is not actually copper... So check that too.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Michelle Konzack avatar image
Michelle Konzack answered ·

If you have to stack lugs, put the one with the highest power first on, then the others.

Then put a washer on and a springwasher (or however this is called in english) and then the nut.


But as @Alexandra mentioned, for security reason use a Busbar.


However, PVC cables starting to give up at 60°C and are gone at 80°C.

Better is the use of welding cables H01N2-D (do not use the -E, because they are much more flexible of finest strands, but if you do not have the right tools, you endup in a nightmare)

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
Yes, spring washer
0 Likes 0 ·
nick5000 avatar image nick5000 commented ·
Thanks, the two black cables goes both directly to the positive battery terminal, so I assume the power should be equal for the two.
0 Likes 0 ·
cpt-pat avatar image cpt-pat commented ·

> Then put a washer on and a springwasher (or however this is called in english) and then the nut.

It's called a "split ring washer."

0 Likes 0 ·
Justin Cook avatar image
Justin Cook answered ·

In addition to the excellent points already made, I'll add that the rotary switch you're using isn't rated to the system voltage you're using it on... No readily-available rotary switches are rated to 58-60V as required for a 48v nominal system.

33 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Michelle Konzack avatar image Michelle Konzack commented ·
Right, only 32Vmax
2 Likes 2 ·
Justin Cook avatar image Justin Cook ♦♦ Michelle Konzack commented ·
I can't tell if that's a Victron switch - if it is, it's rated to 48v max, so could be used on a 36vNom system, but a lot of other switches from BEP and Blue Sea are rated to 32v or 36v max for 24vNom systems... and of course cheap knockoff switches are anyone's guess but under no circumstance suitable for 48vNom systems. Have to go to breakers or mechanical contactors at the higher voltages!
0 Likes 0 ·
Show more comments
nick5000 avatar image nick5000 commented ·

I was told on this forum that this switch is "of course" compatible with 48V systems. Also Victron writes that this switch is for up to 48V systems. Victron also use this switch in their Multi RS drawing with 2 x 25.6V batteries. Why would Victron recommend this switch for the Multi RS if it is actually max 48V?screenshot-2023-12-07-at-132659.png

0 Likes 0 ·
daza avatar image daza nick5000 commented ·
Personally for me I wouldn’t worry about the volts it’s the amps that are going to do the damage, we need to know how yours is wired @nick5000 as this does not look how yours is wired as the two black wires go to the switch with multi wiring can you tell us how yours is
0 Likes 0 ·
Show more comments
daza avatar image
daza answered ·

100% heat damage and it doesn’t look like it’s started from the switch bubbling on the cable or sleeving if that is sleeving, if not I would say the connection to your multi isn’t great as the heat has generated at that end hence bubbling multi end and the discolouration of the insulation that’s if it is not sleeved!

What multiple are you running?

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
The bubbling is at the switch end.
0 Likes 0 ·
daza avatar image daza kevgermany ♦♦ commented ·
The discolouration starts as the multi and the bend in the cable is were it’s bubbled switch end no discolouration
0 Likes 0 ·
Craig Chamberlain avatar image Craig Chamberlain daza commented ·
I think the "discolouration" you mention is actually just a shadow. Look at the shadow on the wall & floor and you'll see it coincides with the change on colour on the cable.

The heat definitely, IMHO, came from the switch end.

1 Like 1 ·
daza avatar image daza Craig Chamberlain commented ·

@Craig Chamberlain could Be but would like OP to show the connection in the multi and exactly what multi it is for the and if the two black cables are also feeding to the multi, but either which way think everyone’s consensus is not to run the system at this point and maybe to bottom out the cause. @nick5000

0 Likes 0 ·
nick5000 avatar image nick5000 daza commented ·
Thanks! I've replaced this cable now. The dual black cables is directly from battery positive, 2 x 25mm2 cables. I think that burned cable was old and bad.
0 Likes 0 ·
k-k avatar image
k-k answered ·

I'm very interested in seeing the cable sawed in halves, to see wether it is copper-clad or real copper.

is it possible to know wether it was new for this application, or was this normal cable used before (wrongly) in a cable-chain and ended months later in the trash-box. After that it was picked up and misused/reused again. Mechanical dead, overburdend with heat by lug stacking. Maybe 10 iD lug on 8mm oD screw above smaller ones from the black cables.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nick5000 avatar image nick5000 commented ·
It was an old cable, so that was probably the reason. I checked it now and it's cracking when I bend it.
1 Like 1 ·
nick5000 avatar image
nick5000 answered ·

Thanks for the replies! I didn't get any email confirmation for the replies, so didn't see all the replies until now.

The cable was an older cable that the installer said was ok. I checked it now and it is brittle and make cracking sounds when I twist it, so I guess this cable is not very good. Also the connection to the Multi was small and poor and looks black. I think it started happening when we connected to shore power for the first time recently, and got around 5000W in together with solar at the max. I'd set max charging to 100A.

I've already replaced this cable, and will also look over all the other cables (and will also avoid charging at 5000W which I don't really need to).

photo-2023-12-07-131527.jpegphoto-2023-12-07-131529.jpeg


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

regman54 avatar image regman54 commented ·
Thanks for additional photos to include the lug. That certainly helps to explain things and I agree with daza, there's not much meat (contact area) in that lug.
2 Likes 2 ·
daza avatar image daza commented ·

If you haven’t replaced the switch at least i hope you cleaned the contacts don’t answer my previous question as you answered here. Still IMO I would worry about the volts it’s the amps but the lug looks like it hasn’t got any meat on it to me which would 100% cause buildup of heat which just leads to more resistance and heat until this happens. Is the cable copper clad and by any chance was that lug soldered? As I would say they are looking like the cause as I see what looks like solder in the cable and on the edge of the lug. Is this the case @nick5000

Spot on to everyone that said switch end, I stand corrected Sir’s ;)

0 Likes 0 ·
kevgermany avatar image kevgermany ♦♦ commented ·
I guess you cleaned all the terminals thoroughly to avoid future problems.

It would be a good idea to keep a close eye on temperatures until you're happy the problem is fixed. That switch is clearly suspect.


0 Likes 0 ·