Dragos asked

3-phase Multiplus II 10000/48 issue when configuring the ESS assistant

Hi, All.

I am the new owner of 3 Victron MP 2 10000/48. I also have one Fronius Symo PV inverter 10KW and 8 Pylontech US3000C batteries. I made the installation and updated the firmware version to the latest one (506). Everything went well, so no issues. I setup the system for 3-phase configuration and sent the configuration to the devices. What I want to achieve is to use the Fronius PV inverter on the MPs output and use the solar power to charge the batteries, for house consumption and the production excess to be exported to the grid. I am located in Romania and I already export energy from the Fronius inverter to the grid. I chose the grid code to be Romania because otherwise I cannot load the ESS assistant and configured the parameters as in the attached files. I saved the configuration to be loaded on the MPs for phase L2 and L3, sent the configuration to MP on phase L1. First issue I encountered was that I cannot load the configuration saved for L1 when trying to configure MPs for L2 and L3. There is a requirement for the grid password. I do not have it, but I tried to configured everything manually and use the same parameters as for phase L1. I noticed that for phases L2 and L3 when loading the ESS assistant it does not ask you for the PV inverter power (it is only asked for L1). Ok, I loaded and wrote the config for the MPs for L2 and L3 and after doing this the inverters do not switch on and send voltage on the outputs. The following LEDs configuration appears: for L1 only the Low Battery LED is on (even if the batteries are fully charged), the rest of the LEDs are OFF, for L2 and L3 the Bulk LEDs are flashing, the rest are OFF. As a remark, the Fronius PV inverter is not yet connected to the MPs output. The Cerbo GX is not yet commissioned/setup and the batteries are not communicating with the MPs via the Cerbo GX device. Can anyone tell me what I am doing wrong?

Thank you in advance. All the best. mp2-3-phase.jpgphase-l1-charger-tab.jpgphase-l1-general-tab.jpgphase-l1-grid-tab.jpgphase-l1-virtual-switch-tab.jpgphase-l1-inverter-tab.jpgess-assistant-battery-capacity.jpgess-assistant-battery-system.jpgess-assistant-dynamic-cut-off.jpgess-assistant-frequencies.jpgess-assistant-pv-inverters.jpgess-assistant-restart-offset.jpgess-assistant-sustain-voltage.jpgess-assistant-total-solar-power.jpgess-assistant-veconfig-settings.jpg

ess settings
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

If you dont have a grid code you cant load ESS.

First time set up allows the selection, you should not need to change it after that.

Did you buy them second hand to try to set up with a different code?

19 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Dragos avatar image Dragos commented ·
They are brand new inverters. They came with None in the Grid Code and since I could not load the ESS assistant I chose the Romanian Grid Code. But, after saving the configuration to a file (for loading it onto the next 2 devices for phase 2 and 3) I cannot to that because the grid password is required. Anyhow, I configured manually the ESS for all 3 phases, but after sending the configuration to the devices, they stopped working. And my question was, why this behaviour?


0 Likes 0 ·
Show more comments
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Recommended settings and more for Victron + Pylontech:

https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ponzoa avatar image ponzoa commented ·
connected to his system and sorted it out. All good now. Thanks.
0 Likes 0 ·