3 x Multiplus 10000 ii + 1 x Central 15kWh Pylontech

Hello,


Just wanted to double check something.


I am designing a system that is 3 phases 230v L-E and I am proposing putting 1 inverter on each phase and then having a central battery bank of 3 x US5000 Pylontechs.


There will be 3 sets of battery cables going to the Victron Lynx from the inverter ( 1 pair per inverter ) and then a set going from the lynx to the battery.


IS there any reason why this wont work?


Just wanted to double check.


Thanks.

Multiplus-IIPylontechmultiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
nickdb avatar image
nickdb answered ·

Yes, you are grossly undersized on the batteries which can deliver around 240A on a system that could use over 600A.

And that is assuming US5000C. US5000’s have lower discharge specs.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
Agreeing with @nickdb on all points.



Also..... L- E as no neutral. Big no to that. That is a delta connection it is not supported.

0 Likes 0 ·
jordant2612 avatar image jordant2612 Alexandra ♦ commented ·
Thanks - Yes there will be a neutral there of course.


customer wanted 10kW inverters and 15kWh batteries. So I mean it’ll work it’ll just drain the batteries quick and if he wants more batteries he can.

0 Likes 0 ·
nickdb avatar image nickdb ♦♦ jordant2612 commented ·

No. The BMS will protect and the site will go dark. Its not a capacity issue, it’s a supply problem.

Letting an end-user dictate a configuration is a great way to end up with issues. Hope you protected yourself in writing.

Good luck.

0 Likes 0 ·
Duivert NL avatar image
Duivert NL answered ·

thats not going to work ... as @nickdb stated, 15kW is not enough, you need at least to triple that amount

i have a 3 phase multiplus 2 3000 system and 15kW pylontech battery storage and thats the recommended minimum


see this document: https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jordant2612 avatar image jordant2612 commented ·
Thanks. I’ll either down size the inverters or increase the battery capacity. So if I’ve got 3 x US5000 commoned up to 3 inverters. Does that document means it’s 1 battery to 1 inverter or 3 batteries to 1 inverter?
0 Likes 0 ·