Neutral Earth Bond in 230v Victron Phoenix 24/3000

I have purchased an older used Phoenix 24/3000 230v inverter. I've set it up for testing and it seems to work well. My meter shows 230v between the active and neutral and approx 114v between neutral and earth, and 116v between active and neutral.

The manual is very vague and makes no mention of whether or not the earth can be bonded with the neutral. Seeing 114v on my neutral suggests to me that inverter is of the split phase twin active variety, and if I were to earth the neutral I would essentially be placing a dead short on unit.

Does anyone know if earthing the neutral is safe/will work?


The serial number of the unit is 0850317012

Grounding
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tilo avatar image tilo commented ·

The current model has an internal connection between Neutral and Earth (inverter enclosure which is also the grounding point). You might try with a resistance making a connection between Neutral and Earth, for example with an incandescent light bulb. If you measure no current, and if the voltage difference between Neutral and Earth disappears, then I assume you can connect Neutral to Earth without provoking a short circuit.

As Victron is about 40 years old, it might help to know how old your model is. The serial number can give a hint about the age of the inverter. Can you post the serial number? Some "veterans" then could help further, if in the past existed models that had no internal Neutral to Earth connection.

0 Likes 0 ·
Show more comments
1 Answer
jacob89 avatar image
jacob89 answered ·

So I've found an answer to my own question. I put a light bulb between neutral and earth, and it did not light at all. Measuring between active and earth with the bulb in place I now had 230v between active and earth.

So I felt safe to try a link between neutral and earth, and it gave me the results I wanted.

It is safe to bond neutral and earth with this inverter.