MPPT 100/20 grounding the loads

I am in the process of wiring up my 100/20 mppt controller to a deep cycle battery, 3 x 80watt PV wired in series and a fuse box which will power my accessories including a fridge. I presume I’m correct in thinking that my battery will charge my accessories through the controller when the solar is insufficient? Also do I need to send the ground wire back to the controller from the fuse box or can I ground directly back to the battery? Thank you

MPPT ControllersGrounding
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Margreet Leeftink (Victron Energy Staff) avatar image
Margreet Leeftink (Victron Energy Staff) answered ·

Hello,

Yes your presumptions are correct. Your accessories will be fed by solar power during the day. This will be complimented by battery power during cloudy weather or completely by battery power during night.

The ground wire from the accessories should be connected to the MPPT controllers load output negative.



2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

joeoffgrid avatar image
joeoffgrid answered ·

All negative terminals on my blue solars are same potential. So why not use a common minus?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

MPPT Product Page

MPPT Error codes

MPPT 150/60 up to 250/70 Manual

Ground, earth and electrical safety


Additional resources still need to be added for this topic

Additional resources still need to be added for this topic