Good evening everyone,
I have 2 strings of 7 panels each on the MPPT RS 450/100
Im planning to add more ,should I make it 2x9 panels or 2x10?
What margin of safety to keep regarding max Voc?
Panels are canadian solar 410w -Voc 37.2,Isc 14.01
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Good evening everyone,
I have 2 strings of 7 panels each on the MPPT RS 450/100
Im planning to add more ,should I make it 2x9 panels or 2x10?
What margin of safety to keep regarding max Voc?
Panels are canadian solar 410w -Voc 37.2,Isc 14.01
@ukXan As per the manual re note 1, what is your battery float voltage?
Voc goes up with lower temperatures. What is the lowest temp your array will experience?
Perhaps use the mppt calculator?
Pylontech battery float as per victron documentation is 51 V
Many thanks,
I too have the RS 450/100 (well x2) and x9 panels on each tracker and live in the same area as you. Over the coldest sunny day when on float i was still well within spec of the 450/100 a and my voc is a bit higher than yours so i would say x10 on each tracker but as suggested check the calculator first.
The only other thing to consider is shading if x10 have one shaded you might be better off with x9.
Dave.
This is just what i have seen and not a recommendation or suggestion you need to make up your own mind.
So in summary would 9 panels on each tracker be safer then given Voc 37.2,Isc 14.01?