Good evening everyone,
I have 2 strings of 7 panels each on the MPPT RS 450/100
Im planning to add more ,should I make it 2x9 panels or 2x10?
What margin of safety to keep regarding max Voc?
Panels are canadian solar 410w -Voc 37.2,Isc 14.01
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Good evening everyone,
I have 2 strings of 7 panels each on the MPPT RS 450/100
Im planning to add more ,should I make it 2x9 panels or 2x10?
What margin of safety to keep regarding max Voc?
Panels are canadian solar 410w -Voc 37.2,Isc 14.01
@ukXan As per the manual re note 1, what is your battery float voltage?
Voc goes up with lower temperatures. What is the lowest temp your array will experience?
Perhaps use the mppt calculator?
Pylontech battery float as per victron documentation is 51 V
Many thanks,
This is just what i have seen and not a recommendation or suggestion you need to make up your own mind.