Add 6 panels to MPPT RS 450/100

Good evening everyone,

I have 2 strings of 7 panels each on the MPPT RS 450/100

Im planning to add more ,should I make it 2x9 panels or 2x10?

What margin of safety to keep regarding max Voc?

Panels are canadian solar 410w -Voc 37.2,Isc 14.01

Canadian-Solar_395-420W.pdf


mppt rs
9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

@ukXan As per the manual re note 1, what is your battery float voltage?

Voc goes up with lower temperatures. What is the lowest temp your array will experience?

Perhaps use the mppt calculator?

1 Like 1 ·
Show more comments
dbainbridge avatar image dbainbridge commented ·
It would be fine since the highest Voc even at -6C would be 402V with 10 of those panels in series. The issue you would have is with 2 strings of 10 panels in series would result in rated power of 8200W. Each tracker on the MPPT RS can only handle max of 4000W so you'd potentially lose over half the power. It would be much better to keep it to single string of 10 for both trackers. Even then you will run into the maximum amperage of MPPT RS of 100A since that 8200W would be well over 100A charging capability. Everything would still work you will just be losing a lot of potential power if you need it.