MultiPlus-II randomly starts inverting for less than a minute

I have installed the MultiPlus-II 48/5000/70-50 (v500 firmware) inverter with Pylontech US5000 battery and Cerbo GX (v2.92). While browsing data in Remote Console I noticed that for unknown reason MultiPlus sometimes starts inverting during up to 1 minute when the grid is up and has normal voltage.
vrm-victronenergy-installation.png Is it some sort of internal self-test that inverter periodically does or is it a sign of issue?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
nickdb avatar image
nickdb answered ·

Looks like grid rejection. Can be any number of reasons, usually a sign of a poor grid supply. If you’re connected in real time with a mk3 the ve bus monitor should show why, but it’s next to impossible to get the timing right.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rost avatar image rost commented ·

Thank you for your input. Yeah, those issues mostly happen during night so it is impossible to catch it live with MK3. The grid supply is indeed poor, that's why I have installed a double conversion voltage stabilizer, so I suppose even tiny issues in grid supply must be eliminated due to double conversion in the stabilizer.

0 Likes 0 ·
nickdb avatar image
nickdb answered ·

@Rost If you connect to the system with a mk3 adapter and veconfigure, go to the grid tab and under the grid selection you choose "show NS protection log".

The inverter keeps the last 5 reasons for grid loss/rejection in NVRAM.

You can also show the criteria that the grid code is enforcing by choosing the grid code settings tab.

Between these two, you should be able to identify why your system is behaving the way it is.

(sorry for the rough mobile pics)

screenshot-2023-02-18-at-140114.pngscreenshot-2023-02-18-at-140127.png


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rost avatar image rost commented ·

@nickdb Thank you for the screenshots. Fortunately this anomaly happened recently so I was able to follow your advice and check the log. Sadly all recorded events happened days before the recent anomaly and corresponded to confirmed grid outages (at VRM there was a dip of input voltage at those timestamps as well). Sending another screenshots of VRM zoomed at recent anomaly and NS log.vrm.png

log.png

0 Likes 0 ·
vrm.png (304.8 KiB)
log.png (142.5 KiB)
nickdb avatar image nickdb ♦♦ rost commented ·

@Rost would you mind if someone had a look remotely? Could you share the VRM portal ID?

0 Likes 0 ·
rost avatar image rost nickdb ♦♦ commented ·
@nickdb Sure, please send me their emails and I'll add them to my VRM installation.
0 Likes 0 ·
myvicrocks avatar image
myvicrocks answered ·

@Rost Did you ever find an answer to this. I have the Multi II 10kva and this is driving me absolutely nuts. I get these 1min inverting randomly I noticed mostly during the night 1 to 2 hours appart.


The data doesn't show any drop in V or Frequency from the AC side. I have almost rewired the entire house looking for a rougue neutral or live.

@nickdb - did you ever check remotely an see anything? I saw your screenshots had ZA grid listed. I'm in ZA as well. This is driving me dam nuts I'm about to pay an absurde amount of money to have a logger installed on my AC side to see why the hell the inverter keeps inverting for 1min. Happy to let anyone check remotely as well.


Can one see the NS protection log remotely (i.e. not being connected via Mk3?)


This is just in a space of 24 hours:

screenshot-20230323-170124-vrm.jpg


27 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
Hi, you have to connect via a mk3.

Unfortunately in really short outages it doesn't seem to log. It will be one of the parameters in the grid code getting out of whack. The worse the grid is, the more likely it happens.

Mine aren't as often. I suspect it might be an impedance issue but ultimately it is a grid fault.


0 Likes 0 ·
myvicrocks avatar image myvicrocks nickdb ♦♦ commented ·

Thanks @nickdb - well in ZA I would not be surprised at all. Any suggestions which parameters on the grid code I should check first / tweak.


Impedance from/on the grid?


I am in ZA but not using the ZA grid code as I have used the following, happy to take any guidence on any of the parameters to tweak, despreate now on these multis II mini-inverts going on as those relays and contactors are dam loud on the Multi II 10KVA :)

veconfig.png

0 Likes 0 ·
veconfig.png (80.2 KiB)
rost avatar image rost commented ·

@myvicrocks I've sent @nickdb my VRM id in February but didn't get any feedback since then. This random switchovers continued to happed once every day or two.
I recently installed a several solar panels and switched my system off-grid so at least for now this issue does not bother me at all.
What I can also add is that this is definitely not some reporting or dashboard bug. I once was near the inverter when this happened and it really switched to the inverting mode for 20 or 30 seconds.

0 Likes 0 ·
myvicrocks avatar image myvicrocks rost commented ·
Thank you @Rost that I know as well I'm often near the inverter and hear the contactors and relays doing their dance. I am sure it's going to Invert mode for that 30s / 1min, I was trying to figure out why. I have had my entire DB board rewired (I knew there wasn't a issue but wanted it neater and incase we found it there) had three different electricians check the feed from the "street feed" all the way to the house and none of them could find a fault.


Hence why I started searching

0 Likes 0 ·
Show more comments