MultiPlus-II randomly starts inverting for less than a minute

I have installed the MultiPlus-II 48/5000/70-50 (v500 firmware) inverter with Pylontech US5000 battery and Cerbo GX (v2.92). While browsing data in Remote Console I noticed that for unknown reason MultiPlus sometimes starts inverting during up to 1 minute when the grid is up and has normal voltage.
vrm-victronenergy-installation.png Is it some sort of internal self-test that inverter periodically does or is it a sign of issue?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
nickdb avatar image
nickdb answered ·

Looks like grid rejection. Can be any number of reasons, usually a sign of a poor grid supply. If you’re connected in real time with a mk3 the ve bus monitor should show why, but it’s next to impossible to get the timing right.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rost avatar image rost commented ·

Thank you for your input. Yeah, those issues mostly happen during night so it is impossible to catch it live with MK3. The grid supply is indeed poor, that's why I have installed a double conversion voltage stabilizer, so I suppose even tiny issues in grid supply must be eliminated due to double conversion in the stabilizer.

0 Likes 0 ·
nickdb avatar image
nickdb answered ·

@Rost If you connect to the system with a mk3 adapter and veconfigure, go to the grid tab and under the grid selection you choose "show NS protection log".

The inverter keeps the last 5 reasons for grid loss/rejection in NVRAM.

You can also show the criteria that the grid code is enforcing by choosing the grid code settings tab.

Between these two, you should be able to identify why your system is behaving the way it is.

(sorry for the rough mobile pics)

screenshot-2023-02-18-at-140114.pngscreenshot-2023-02-18-at-140127.png


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rost avatar image rost commented ·

@nickdb Thank you for the screenshots. Fortunately this anomaly happened recently so I was able to follow your advice and check the log. Sadly all recorded events happened days before the recent anomaly and corresponded to confirmed grid outages (at VRM there was a dip of input voltage at those timestamps as well). Sending another screenshots of VRM zoomed at recent anomaly and NS log.vrm.png

log.png

0 Likes 0 ·
vrm.png (304.8 KiB)
log.png (142.5 KiB)
nickdb avatar image nickdb ♦♦ rost commented ·

@Rost would you mind if someone had a look remotely? Could you share the VRM portal ID?

0 Likes 0 ·
Show more comments
myvicrocks avatar image
myvicrocks answered ·

@Rost Did you ever find an answer to this. I have the Multi II 10kva and this is driving me absolutely nuts. I get these 1min inverting randomly I noticed mostly during the night 1 to 2 hours appart.


The data doesn't show any drop in V or Frequency from the AC side. I have almost rewired the entire house looking for a rougue neutral or live.

@nickdb - did you ever check remotely an see anything? I saw your screenshots had ZA grid listed. I'm in ZA as well. This is driving me dam nuts I'm about to pay an absurde amount of money to have a logger installed on my AC side to see why the hell the inverter keeps inverting for 1min. Happy to let anyone check remotely as well.


Can one see the NS protection log remotely (i.e. not being connected via Mk3?)


This is just in a space of 24 hours:

screenshot-20230323-170124-vrm.jpg


27 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
Hi, you have to connect via a mk3.

Unfortunately in really short outages it doesn't seem to log. It will be one of the parameters in the grid code getting out of whack. The worse the grid is, the more likely it happens.

Mine aren't as often. I suspect it might be an impedance issue but ultimately it is a grid fault.


0 Likes 0 ·
myvicrocks avatar image myvicrocks nickdb ♦♦ commented ·

Thanks @nickdb - well in ZA I would not be surprised at all. Any suggestions which parameters on the grid code I should check first / tweak.


Impedance from/on the grid?


I am in ZA but not using the ZA grid code as I have used the following, happy to take any guidence on any of the parameters to tweak, despreate now on these multis II mini-inverts going on as those relays and contactors are dam loud on the Multi II 10KVA :)

veconfig.png

0 Likes 0 ·
veconfig.png (80.2 KiB)
rost avatar image rost commented ·

@myvicrocks I've sent @nickdb my VRM id in February but didn't get any feedback since then. This random switchovers continued to happed once every day or two.
I recently installed a several solar panels and switched my system off-grid so at least for now this issue does not bother me at all.
What I can also add is that this is definitely not some reporting or dashboard bug. I once was near the inverter when this happened and it really switched to the inverting mode for 20 or 30 seconds.

0 Likes 0 ·
myvicrocks avatar image myvicrocks rost commented ·
Thank you @Rost that I know as well I'm often near the inverter and hear the contactors and relays doing their dance. I am sure it's going to Invert mode for that 30s / 1min, I was trying to figure out why. I have had my entire DB board rewired (I knew there wasn't a issue but wanted it neater and incase we found it there) had three different electricians check the feed from the "street feed" all the way to the house and none of them could find a fault.


Hence why I started searching

0 Likes 0 ·
nickdb avatar image nickdb ♦♦ myvicrocks commented ·

We looked at rosts install but its impossible to get data remotely and vrm isn’t designed for this.

An electrician will check voltages but little else and the reality is these conditions are grid related and transitory, so you’d have to be connected in realtime which isn’t practical. Even knowing the issue, there is little you can do about a weak grid. It’s annoying but the way it is.

A logger will provide some clarity, but it is an expensive intellectual exercise.

0 Likes 0 ·
myvicrocks avatar image myvicrocks nickdb ♦♦ commented ·
Again, thank you for the input. I don't even know where to start. Calling out the municipality to come and diagnose and "fix" will be like finding a cure to covid in ZA.


Quick question in your screenshots above I saw you were using the grid code for ZA, I noticed it has wider ranges example under voltage 195.5V where currently I am using AC low disconnect at 208V.

Questions:

1. On the grid code settings what I would think would trigger the inverter to invert would be the under voltage and/or frequency changes out of the set range. Is there any other setting that would trigger the inverter to change mode to inverting? I know it's academic but I want to run the logger so would like to know what I am checking.

2. I read up on the "weak AC" setting it seems to change the algorythm on monitoring AC input, would this help in any way?

3. I see you used the ZA Grid code, have you experienced any issues using this grid code? My installer chose the settings I have above as they have experienced "issues" with the ZA grid code.

I am using pretty beefy batteries x2 BSLBat 15.4kw

0 Likes 0 ·
nickdb avatar image nickdb ♦♦ myvicrocks commented ·
Hi, sorry missed this.

I've not had issues with the grid code.

I have actually recorded the same symptoms, at the same time, on systems within a 10km radius of me, so I am sure it is the grid.

It is not voltage related, though we have serious low voltage issues here, and I am still on defaults.

Check your NS log and see if it is being recorded, just don't leave it for too many loadshedding outages as the log only tracks the last 5 events.

Weak AC won't help, it is for generators and causes other issues.

0 Likes 0 ·
myvicrocks avatar image myvicrocks nickdb ♦♦ commented ·

Thanks for the response.


I guess I am going to just have to life with the issue, nothing else I can physically do on my system. It's a pity as the relays and contactors are pretty loud.

What I noticed was when it happens a lot in quick succession (which does happen sometimes), it ends up tripping the earth leakages of the essential loads. Not sure if somehow inverting , not invertering in quick succession (i.e. 3 times in a row within 5 mins) which I sometimes gets, creates something on the electrical essential loads and the earth leakage drops.


I am going tongive the ZA grid code a go as the variances 195.5V on unde rvoltage is much broader than the one I have now with 208V for AC low disconnect. (Are these two the same parameters under voltage & AC low disconnect?

I do wish there was an "advanced" option Victron would allow as a setting on VRM to be able to diagnose in these cases.

Another question: on your screen shot I can see the tab you on to get the NS Protect values, it it just a button on that tab?


I had two days of no micro-inverting and today...

screenshot-20230325-115105-vrm.jpg

0 Likes 0 ·
nickdb avatar image nickdb ♦♦ myvicrocks commented ·

If your earth leakage is tripping on grid return also go look how many surge protection multiplugs you have, these can contribute. Do you have surge protection in your db? If so what model? Some can be too sensitive, Schneider works well, Hager not.


NS log is a button you press on that tab.

0 Likes 0 ·
myvicrocks avatar image myvicrocks nickdb ♦♦ commented ·

You know @nickdb glad you mentioned surge protection on the DB I had (cheap ACDC ones) on the incoming feed, but in the quest of trying to stop this dam micro inverting I had my electrician rip out my entire DB, to back to basics remove all surge protection etc, I even had those little breakers that has a light that indicates if the grid is on or not I took everything out.

Poor guys spent 1 full day (till 8pm) rewiring everything matching each live with its neutral and labeling everything. With the false hope this dam micro inverting would stop.

I wonder if this micro inverting damages the relays etc since it's frequent and just for 30s to 1min.


I'll check that NS protection log when I am home (away for a few days). I am sure the micro inverting will carry on doing its thing.

0 Likes 0 ·
nickdb avatar image nickdb ♦♦ myvicrocks commented ·
Don't worry, the relays will be fine, they are specced for worse.

If you are software savvy, you could deploy victron's grafana docker container which gives granular data, so more accurate than vrm which averages over 1 minute.

0 Likes 0 ·
myvicrocks avatar image myvicrocks nickdb ♦♦ commented ·
@nickdb - I am pretty software dev savvy :) I had it up and running before just didnt persue it nor did I know how often it was refereshing vs VRM.


I have 2 or 3 PI4 lying around I will get one up and running just to do this.


I know this is a dumb question but which data / area / Panel would I be monitoring to see what or where this micro - inverting is coming from>

0 Likes 0 ·
nickdb avatar image nickdb ♦♦ myvicrocks commented ·
Grid stats, so freq, voltage. It is a transient that sets it off.

It is too quick for VRM. That's about all the unit tracks.

Grafana collects every couple of seconds, so you have better visibility.

0 Likes 0 ·
myvicrocks avatar image myvicrocks nickdb ♦♦ commented ·
Will set it up tomorrow and get it going. See if we can see the Grid V or Frequency drop for a split second.
0 Likes 0 ·
Show more comments
rost avatar image rost nickdb ♦♦ commented ·
@nickdb Is there a possibility that Victron engineers would create a special firmware build with additional logging that @myvicrocks and I could install and gather the necessary data?
0 Likes 0 ·
myvicrocks avatar image myvicrocks rost commented ·
Don't think it needs special software, infact VRM and the Cerbo is good enough to log the info like a MK3 does. It's about the refresh rate they saving the data even in "real time" it seems to save data every 2mins (I could be wrong).


I do agree though things like the NS protection Log should be data one can download off VRM. Even if it's a "advanced" feature one has to turn on for a period to be able to do detailed remote logging.

Of course this is all at the helm of Victron wanting to enable this or prioritising it over other important features they have in the pipeline.