Hi, new here, but not to off grid.
I have been running a Multi II with pylontech 3000c`s for a year after selling my old outback/lead acid set up
Impressed in many ways having been an off grid user since 1998
However having issues with L.O.M messing my SR7 AVR regulators around
My current set up is Grid/Generator (1500rpm kuboata with Meccalte 4pole 7Kva), Multi II with just the one AC in
Despite reassurances at time of purchase the Multi`s L.O.M screws around with the regulator and in all scenarios either puts the Multi in Passthru or spits out completely, on hindsight i needed 2x AC in but had never had any problem with Outback or Trace re anti islanding
I`m familiar with the Victron L.O.M article but find the idea of having to shell out for a Ziehl anti islanding relay somewhat.... "insulting"
I know my generators, Ive lived with them commercially on farm since 1998 coupled to SW Traces and VFX Outbacks, with or without grid with no issues.
IMHO the Victron L.O.M in an attempt to push the Hz messes with the SR7`s voltage stabilisation, it being Voltage fluctuations that make the Multi spit out its dummy.
YES, If I use "grid other" with L.O.M disabled everything is sweet as sweet..
I understand the concept of islanding, so running "grid other" L.O.M disabled is not an option, neither is £500 for Ziehl.
Has anyone found a compliant alternative or solution to this issue?
The SR7 is not at issue Ive tried it with a new unit
Im considering using an "under voltage release" din rail device which couples with a 2 pole MCB placed between grid and Multi, grid fails device trips, I dont need to automatically re-connect, i just need to prevent back feed into a damaged grid, has anyone used this method?
Thanks