Three phase system shutdown on auto gen start

20230125-103944.jpg

This three phase system connected with a 40/28 Freedom Lite lithium battery recently shutdown and starts up whole system on auto generator start after sensing low SOC. Please what is the possible solution?

generator auto startshutdown
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@Noah

More details are needed about the system. I would wonder if it is not because the battery is marginal or too small.

How low is the SOC? Do you have bad cell imbalances? does this happen when there is no solar i.e. at night? Is it happening when a larger load switches on at the low SOC?

Why not start the generator automatically before the system gets to thevlow SOC?

Can you supplier or dealership not help? It looks like a complex system.

0 Likes 0 ·
1 Answer
noah avatar image
noah answered ·

SOC was set low to 50% for auto gen start and gen stop at 99%. I cannot say about the individual cell behaviour because battery pack is compact. The system was installed three years ago for a banking hall so more daytime activities. Fault shutdown and self restart only occurs during auto gen switching. AC output Load is about 9,000 to 20230125-115822.jpg10,000 watts averagely. Three units of fronius 5kva, three units of multiplus 5kva, 40kw lithium battery freedom lite single pack. The fault started two weeks ago.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
In the VRM advanced, you will need to load up some widgets to see the battery information. Or download the csv data.

When the generator switches on there will be a power assist happening as the system synchronises so could still be a battery issue.


It may be worth updating the firmware and reprogramming the inverters and system components. In three years the error reporting among other things has improved.


0 Likes 0 ·

Related Resources

Additional resources still need to be added for this topic

Cerbo GX - Generator auto start/stop

Automatic Generator Start/ Stop [PDF]

Automatic Generator Start/ Stop [Online]

Which relay and control to use?

How to wire generators with a three wire interface.

Additional resources still need to be added for this topic