I have my EV Charger wired to the relay output of my Cerbo GX. I can now switch it on / off manually via the vrm portal but it would be great if there was an option to assign it to the SOC or other values such as Battery load and have it switch automatically.
You can also use the relay on a smart shunt or bmv to achieve the SOC switching.
Or have the charger on AC2 of an inverter that is also programmable on SOC
Hello @Alexandra, interesting your comment.
Would you be so kind to help me find more information about this option? I am quite new with my installation and need to manage SOC to stop discharging the battery when I charge my EV. Today I have to manually change to "keep battery charge" or increase the SOC %, but I would like to have something more automatic.
You can use the programmable relay to switch ac2 out on and off. Here is just an example, obviously you can change the SOC figures to suit what you want.
Then you will have to wire it onto the output 2 of the inverter.
When you run through the wizard for setting it up, you will also see ac loads state and quite a few other options can be used to determin if you want it on or off, such as the one you see above saying if AC1 is available it must also be on.
Thank you! Do you think I can use this feature to stop battery charge/discharge when I start charging the EV? Seems that the ACOut2 relay is more to start charging the EV, but my need is more disactivating the batteries.
If so, where can I find the right configuration guide from Victron? I am wondering for example if I need to activate the DVCC or not.
Thanks
I would do this in NodeRed. You can have it disable ESS discharge when the ev is charging and return back automatically when the EV is done.
This runs on the Cerbo, you just need to Enable NodeRed in the large features menu.
Thank you! If I understand well:
- I need to wire the EV charger onto the output 2 of the inverter
- I need to activate and configure the NodeRed.
If this is correct, where can I find a Victron user manual for activating and configuring NodeRed in the Cerbo?
I use the relais output of one (I have 3 with 6,78kW total) of my SmartSolar to switch on a 3,6kW EV charger (I have only to switch on a Relays which switch a standard wall socket.
It switch on, if the SmartSolar goes into float.
Maybe it is even better to use Absobtion.