When putting two 3000VA Multiplus II in parallel does it become 6000VA
So here is the scenario.
Two 3000VA Multiplus II inverters are in parallel.
No AC input.
Only Battery input.
This is an off grid application.
The multiplus inverters are in parallel to make 240V split phase.
Then they go to the AC distribution panel.
This is a 50 amp RV.
The AC Distribution panel is separated. One leg on one side and one leg on the other so basically as I understand it that is 3000VA on one leg from one inverter and 3000VA on the other leg.
Does this mean that you can only put a 3000VA load on on leg or the other.
Meaning if you end up with a 5000va load on one leg and a 2000va load on the other would you overload the inverter that is getting hit with 5000va or would it look at both Multiplus II inverters as one single inverter like it is a 6000VA inverter and just distribute the overload to the other inverter?