Zero feed-in with ESS, SMA and no AC-IN usage

I just install a Multiplus-II in Papua New Guinea where blackouts and brownouts happen on a daily basis. It is installed on my house which is located on a college campus with other houses. We have enough sun here that I can run disconnected from the grid which I have been doing since the install was completed. Batteries are still 70% in the morning and fully charged by 11:30am. I want to use my excess solar to assist the campus. So my goal is to:

  1. Each morning, charge my batteries to 100% solely from solar before sending power to the campus.
  2. Once the batteries are 100% charged, send the extra solar to the campus which is connected to AC-IN.
  3. Never use the AC-IN to power my house or charge my batteries unless my batteries are depleted.
  4. Never use my batteries to supply power to the campus.
  5. Achieve zero feed-in to the grid.

I have the added complexity of another solar system on someone else's house as noted in the diagram. I understand that the GX can monitor the SMA by using the WebConnect module to help with the frequency shift power control.

It sounds like a fairly simple scenario, but with all of the options available in the ESS assistant, and the possibility of damaging equipment that is not mine, I want to make sure it is setup correctly. As far as having a qualified installer....well we are located way out in the bush, about 450km from the nearest authorized installer. It would take someone a plane ride to get here.

I have downloaded and installed the ESS Assistant. But when it started asking about the frequencies of the other inverter, I uninstalled it and ended up here asking this question. I do have permission from the owner of the inverter to move forward, but I am looking for some advice on what settings to use, both in the ESS assistant and the ESS settings in the GX (raspberry pi) and how to properly interface to the SMA.

It will be possible to feed-in to the grid once both systems are online which we are not allowed to do in Papua New Guinea. So, I also have a Mutliplus-II current transformer for my house and an ET112 energy meter with Zigbee transmitters for the campus meter.

Missing from the picture is a GX (raspberry pi), Lynx power in module, and Smart Shunt.

ac-couple.png

ESS
ac-couple.png (438.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Andy avatar image
Andy answered ·

You're saying, you're not allowed to feed any power back to the grid. How does the campus AC coupled solar avoid that if it produces more power than is being used on the campus? Or is it that underrated that this just not occurs?

The ESS assistant is asking for the frequency of the inverter in case you have one installed on your side of the meter like in this example below. If the grid fails the Multi can control the output of the AC inverter through frequency shifting, depending on your load and battery SOC.

ac-coupled-pv-on-output.jpg

Back to your graphic. You will not have any control from your system to the SMA inverter to control its output. It will just pump out as much power as it can from the solar connected.

You have installed your Victron meter after the campus meter, so your GX should know how much power is needed on the whole campus and then adjust the Multi accordingly. You have to basically turn off your Multi once the batteries are full and let it export your solar to the campus grid with a zero feed in setting. Not sure if this can be programmed with ESS and the Multi. Seems like a complex task. Once you have a meter installed, the Multi always tries to keep it at zero, so will use your battery to power the load (campus).

But I'm not a 100% expert with the Multi and ESS, just from what I read and understood...


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cobraphil avatar image
cobraphil answered ·

Thank you Andy for your thoughts.

The SMA system alone would never be able to produce enough power to feed-in to the grid. But with both systems together, it is possible.

So, in the ESS assistant, do I select the option that an inverter is not connected? In that case, do I need to worry about the two inverters syncing up when both are exporting to the campus power gird? That is one of my main concerns, that the two inverters are not fighting one another or causing damage if one is trying to "outrun" the other.

I do have experience in programming. So if I need to move to mode 2 or 3 of the ESS system and write some node-red code, I am comfortable and willing to do that. But if that is not necessary, and I can set parameters to accomplish my goals, that would be best.

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

shaneyake avatar image shaneyake commented ·

The other inverter won't have any issues as it directly connected to the grid.

You will need some way to monitor the campus grid usage so you can throttle your system up and down. You will need to run Mode 3 to prevent the system from discharging the battery to cover campus usage.