Suddenly I got an error #11 in the system that has been running for weeks without a problem.
It is 3 phase system with 2 MP-2s per phase.
Phase 1 has EasySolar-2 as a master and MP-2 as a slave.
Remote console shows the following:
Maybe someone will help me pinpoint the location of the fault?
What it is a "PE2 closed error"
What it is "Phase L1 device 1 (0)"
What it is "Phase L2 device 1 (1)"
What it is "Phase L1 device 2 (3)"
I thought that "GND Relay Error" has a number 8 but system reports only error #11.
Going by the suggested "Steps"
Step 1: Make sure that the units have been updated to the latest firmware version.
- Inverters FW is 481, GX FW is 2.72
Step 2: Verify that system is properly wired to your installation and your local codes.
- system worked for weeks. Last week one inverter was replaced but there were no errors after replacing.
Step 3: Disconnect the L and N wiring from the ACout terminals.
- breaker at the AC-out disconnects all loads and with loads disconnected there is still error #11.
Step 4: Check your Neutral-out connection. In most cases there should be no external connection between ACin-Neutral to ACout-Neutral, or to Earth.
- There is no connection between AC-in and AC-out neutral wires.
Step 5: Neutral and line input might be inverted. Check the input connections, swap them if needed and retry. In this case, “Failing step: 8” will show.
- it is a working system. Wires would not swap places by themselves.
Disconnecting AC-in makes the error #11 not happen and system is properly working in inverter mode.
What went wrong?
Best Regards,
Marek