Running a Multiplus II 48/3000 35 with only one US3000 Pylontech battery in an Off-Grid System?

Hi Victron Comunnity!

I am installing the following system:

1 Multiplus II 3000/48 35

1 Pylontech US3000

1 MPPT Bluesolar 150/70

1 Venus GX

3000 watt in solar panels


The question I do have right now is: Would the system work? Given that the peak current limit of pylontech batteries are 100Amp per 15 seconds, and the Inverter peak watts surge ratting is 6000W (125 Amps for a 48Vdc configuration)?


Thanks a lot!

Multiplus-IIPylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
shaneyake avatar image
shaneyake answered ·

This isn't the best system design but it would work, as long as you don't run really high loads on your inverter. This isn't a good design because under certain load conditions you will trip the battery off.
Also pylontech batteries don't do well close to their limits. I would not run more than 2000W continuous with just one module.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

smandiol avatar image smandiol commented ·
Thanks for the answer! Yes, I understand, that is not the best system, but my client wanted a "first stage" of the project, because of economic limitations. But the advice for my client is to get one more battery and more PV power.