Hi to all
Trying to troubleshoot a charging problem with 2x Multi II 48-5000-70 in parallel Master & Slave. I also have Venus GX connected. The two units have been inverting great for couple months now but I had not used any grid charging my solar takes care of that. I normally switch the multis over to grid at 00.00 - 06.00 to take advantage of cheap rate and save my 1000 Ah FLA battery from cycling too low. Today, I decided to switch on the charger on the Master Multi to test charging and at 00.00 when the grid kicked in I see the Master go in to Bulk phase but... only 7-10A of charging ?? I realise by default the Multis only charge at 75% as when I only had one unit I never seen more than 53A charging (and I never figured out how to get the full 70A). I was expecting to see about 100A charging with two units in parallel?? The Input AC current Limit is set to 30A (15A on each unit) as my grid supply is 32A. All cables are uniform acoss the two units.
I don't understand why the charging is so low any help to figure out what is limiting the charging current much appreciated as I will need to charge overnight sometimes when the Winter arrives
TIA
PS I also put a DC clamp meter on each units DC cable and they are sharing the charge output, about 4-5A each.