strange behavior Multiplus 2

I would need all of your specialist knowledge. A colleague is running the Victron Multiplus 2 in ESS mode, 10 lead-acid batteries were connected to it. We noticed that a pack (2 * 12V) is no longer in order and then removed it. In the Multiplus we have adjusted the battery capacity. Now it is, however, that he has been continuously discharging the batteries for 2 days without the excess PV power being charged into the batteries. Have I changed something in the settings?

1623844049688.png

Multiplus-II
1623844049688.png (46.2 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@Mixer

Is battery life enabled on the gx device?

And minimum SOC set?

0 Likes 0 ·
1 Answer
mixer avatar image
mixer answered ·

Hi Alexandra,


Thanks for the answer.

I found the mistake.

I unconsciously ticked the store charge, now everything is working again.