Multiplus II behaviour if AC output is connected to AC input

What happens if the inverter output becomes connected to the AC input during failure of grid?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Rob Duthie avatar image
Rob Duthie answered ·

It has anti islanding function so it cant connect to the grid when it goes down. if it did it would over load and shut down as it is powering the grid and your street.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Martyn Duerden avatar image Martyn Duerden commented ·

Hi, thanks for that, if im honest I am still not sure what theat really means...


Scenario


Grid fails, victron provides UPS function from batteries transfer switch moves load to backup therby providing the multiplus with power on its input effectively from its own output, a circular circuit if you like...

Thoughts?

0 Likes 0 ·
Show more comments
boekel avatar image
boekel answered ·

Here's a bit of information about LOM (Loss Of Mains) detection:

https://www.victronenergy.com/live/ve.bus:grid-codes-and-loss-of-mains-detection?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Martyn Duerden avatar image Martyn Duerden commented ·

Thanks for this.

I have done a lot of reading on this lately! it’s all education!