question

fungi avatar image
fungi asked

NiFe battery with multi 24/3000/70 what are the recommended settings

I'm attracted to these batteries as a long term asset. Should I go DC coupled? AC coupled? Where can I find other users with nickel iron experience?

battery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

16 Answers
Paul B avatar image
Paul B answered ·

what do you mean DC coupled AC coupled all batteries ad DC

NiFe referance you will just have to do some google searching, for this info as I dont know anyone using these, at the moment the best options are Lithium Phosphate or have a look at ultra capacitors as these maybe a up and coming option in a few years.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

the term AC or DC coupled is usually about PV installations, AC inverter coupled to the system or DC PV 'charge controller' coupled directly to the batteries.

More information is needed to give an advice on that (grid connected, off grid, etc.)

1 Like 1 ·
boekel avatar image
boekel answered ·

Why would you want to use NiFe batteries? what do you see as an advantage? They have some big downsides like low efficiency, high cost, wide voltage window, low power (charg / discharge), etc.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fungi avatar image fungi commented ·

The advantages are that they are indestructible.

They cost more than some lithium ion batteries but here in Australia they cost less than victron lithium batteries.

0 Likes 0 ·
boekel avatar image boekel ♦ fungi commented ·

Ok, well if you size them so that you don't exceed maximum charge / discharge current...
But you'll have to check if voltage range is compatible with Victron devices, and maybe there is a bms available for them? also if you need special charging curves that are not available you might have to improvise (or maybe a bms can take care of that)

0 Likes 0 ·
boekel avatar image boekel ♦ fungi commented ·

btw, what do you describe as 'indestructible'? the cycle life doesn't impress me much...

0 Likes 0 ·
fungi avatar image
fungi answered ·

20 x NiFe cells in series should be bulk charged to 33v with an absorption time of about 5hrs. They are exhausted at 22v and LVCO is 21.9v

Optimum charging is C/4 up to c/2. Higher rates of charge and discharge are tolerated for short periods and the battery is insensitive to over or under charging.

The main drawback is maintenance. Regular topping up with distilled water.

They have a proven service life of over 50 years and infinite shelf life with careful storage.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

Then you'll have to go for 19 in series, as the Victron inverter/chargers go up to 32 V

'service life' probably in back-up use, not cyclic use.

0 Likes 0 ·
fungi avatar image fungi boekel ♦ commented ·

19 cells has an LVCO of 20.7v

0 Likes 0 ·
Show more comments
fungi avatar image
fungi answered ·

They are used in electric locomotives where they outlast most of the other components. The float voltage is 29v

It is unlikely that I would ever want to charge them with the MultiPlus charger.

More interesting is the inverter's maximum tolerated voltage and whether LVCO can be set low enough.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

do you have a link to datasheets of NiFe cells that are suitable for cyclic use? Might be interesting then.

0 Likes 0 ·
fungi avatar image fungi boekel ♦ commented ·
0 Likes 0 ·
boekel avatar image boekel ♦ fungi commented ·

I can only find charge / discharge information, no information on cycle life (or I'm not looking hard enough)

What I did find is a -terrible- efficiency... worse then lead-acid!

Can you point me to cycle life information?

0 Likes 0 ·
blue-sails avatar image blue-sails boekel ♦ commented ·


From the NiFe sales brochure of:

http://www.hmbattery.com/

0 Likes 0 ·
fungi avatar image
fungi answered ·

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

nothing on cycle life, only on warranty:

Any battery product which becomes unserviceable (not merely discharged) due to defect in material and/or workmanship within the pro-rated period stated below will receive a credit or refund as stated below.

0 Likes 0 ·
fungi avatar image
fungi answered ·

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

tested 250 cycles

0 Likes 0 ·
fungi avatar image
fungi answered ·

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

Ah there's something, good numbers:

Cycle Life 11,000 Cycles At 80% Depth Of Discharge

0 Likes 0 ·
fungi avatar image fungi boekel ♦ commented ·

I would have to decide who to bequeath them to when I die

0 Likes 0 ·
boekel avatar image boekel ♦ fungi commented ·

Ah yes....but they don't give any warranty on the cycle life...

0 Likes 0 ·
fungi avatar image fungi boekel ♦ commented ·

There is so much BS regarding these batteries that wading through it all requires a strong stomach and a lot of spare time

0 Likes 0 ·
boekel avatar image boekel ♦ fungi commented ·

That's why I remain skeptical, I now they're supposed to do great in float-applications...but this 11000 cycles is the only number I could find...and they don't give any warranty on it.

0 Likes 0 ·
fungi avatar image fungi boekel ♦ commented ·

In the modern economic environment most corporate structures don't last long enough to offer that sort of warranty. The company is long gone while the product is still chugging along.

0 Likes 0 ·
Paul B avatar image Paul B fungi commented ·

Maybe , but the product has not taken off in the market place, were the LP version has and its now quite well known and they have great outputs and charge rates , so the its upto you what you select.

NOW the new one on the block though is Ultra Capacitors now 1,000,000 is impressive cycle life

but as far as I can find out the LPs have great life as well

ie and I maybe wrong here but at 80% DOD

after 2000 cycles the LP drop to 80% of original output

after 5000 cycles the LP drop to 70% of original output

after 10,000 cycles the LP drop to 60% of original output

after 50,000 cycles the LP drop to 50% of original output

0 Likes 0 ·
boekel avatar image boekel ♦ Paul B commented ·

What is LP?

0 Likes 0 ·
blue-sails avatar image blue-sails boekel ♦ commented ·

From the NiFe sales brochure of:

http://www.hmbattery.com/

0 Likes 0 ·
fungi avatar image
fungi answered ·

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fungi avatar image
fungi answered ·

Poor coulombic efficiency is not very expensive to overcome considering the cost of pv these days

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

True if you have plenty of room for PV panels yes.

0 Likes 0 ·
fungi avatar image
fungi answered ·

So I would not use AC coupled charging because of the added inefficiency of DC-AC-DC.

Now I need a charger that can be set to 31.4 v absorption for 5hours. I guess victron mppt250/100 can do this???

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image
boekel answered ·

I don't have a 250/100 at hand, but checked with the 150/35 for you, maximum I can set it is 34,78V (so 20 cells might work? - if inverter can handle it)


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fungi avatar image
fungi answered ·

The manual that came with the MultiPlus 24/3000/70 says inverter input range 19-33

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

19 cells is probably better / safer indeed
also to be able to charge with Multi.

0 Likes 0 ·
marekp avatar image
marekp answered ·

Couple years ago I was considering those cells for my solar and backup application.

The main reason was the longevity.
When I looked closely at the process of changing electrolyte in them, I changed my mind.

Lets assume you have 48v/200Ah NiFe battery pack, and you have to change electrolyte because you want them to be new again.

Can you imagine yourself lifting, one by one, 40 cells (200Ah cell weighs over 15kG) turning them over to drain the old electrolyte and than flush the cell with water, drain it and finally fill them with new electrolyte?

The next problem is gassing. They generate hydrogen so you cannot put them anywhere you like.

The next problem is the efficiency of this cell. 60-70% is not much.

For off-grid system somewhere in the woods where there is no grid, the efficiency may not matter, but if the grid is available and you are using ESS system it is a different "ball game".

In some countries, like mine, you can store your summer excess solar energy in the grid and use it within a year with the 20% loss. For me, grid is a "battery" with a 80% efficiency and it is free to install if you have grid connected to your house.

Replacing it with the battery with 60-70% efficiency, and paying for it, makes no economical sense.

Now even their longevity is not the advantage anymore.

If you want longevity buy LTO battery and your grand kids will keep enjoing them. :)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

blue-sails avatar image
blue-sails answered ·

Paul B,

Perhaps he was referring to the way the inverter is setup.

A DC coupled inverter has a much higher than 90% efficiency; however, an AC coupled inverter will have a lower efficiency since the DC energy coming from the solar panels are converted by the inverter connected to the solar panels into AC electricity, and then a second inverter converts the AC electricity to DC to charge the batteries.

Since NiFe batteries have lower efficiency than Lithium batteries, a significant proportion of energy would be lost this way.

If on the other hand there is only one inverter (DC coupled) or charger connected to the batteries there are less losses due to less energy conversions.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

The loss of energy due to efficiency of conversion in inverters is ONE loss in the system.

The loss of energy due to low chemical efficiency of the NiFe battery is the OTHER loss.

One has noting to do with the other.

0 Likes 0 ·
blue-sails avatar image
blue-sails answered ·

@MarekP

NiFe vs Li.pdf

This is a cost comparison per kWh of a Powerwall and a NiFe battery. No inflation or cost changes are included.

The cost of PV, wind, hydroelectric, or grid electricity would need to be tied to this to obtain a more accurate estimate of the cost of producing, purchasing, or / and storing energy.

For those of you unfamiliar with NIFe batteries, I thought of sharing a couple of videos of two people who use them on a daily basis. Each of these video authors has several more videos on the same subject.

One of these authors lives off grid full time with all the modern appliances and an electric vehicle. The second author disconnects from the grid every night.

https://youtu.be/WHxkvf0FZJA

https://youtu.be/2WZ7StJAOuE

Buyer beware: NiFe batteries will be appropriate in some but not all instances.

A feasibility and a suitability analysis may be warranted.


nife-vs-li.pdf (901.0 KiB)
1601643828504.jpeg (218.3 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

@Blue sails

I am not trying to dissuade you from buying NiFe battery. I can see your decision is made.

I am just trying to provide different point of view.

Powerwall is not the only alternative to NiFe.

Maybe add to your comparison other chemistries.

LiFePo4, LiFeYPO4, LTO, NMC.

You will see that the NiFe will not look so good when compared to them.

In your table the self discharge rate is missing. NiFe is not a champion in this regard.

Maybe add to it the cost of the work needed (water adding) to keep NiFe batteries running and the cost of the place where you will be able safely keep them (hydrogen explosion risk) and also the size of it (the sq. meter of any building has its price).

As you mentioned, the cost of energy put into the battery should be taken into account because from NiFe battery you will only get 60% of it back, and only if you take it out quick because self discharge will "eat" additional energy.

The process of changing the electrolyte is not simple, and it is the only reason those cells can be considered long living.

I watched both films, you posted links to.

In first we learned that NiFe are perfect, but no real data to prove it.

In second there is very in depth comparison of couple chemistries, but the application is a totally off-grid system.

I noticed one funny thing.

The author said that he, some time ago, bought NiFe batteries from Hungary.

Why he is not using them anymore, and he replaced them with ones from China.

What happened to those long-lived (eternal) batteries bought from Hungary?

EDIT:

I looked at PowerWall 2 specs and they are different from what you are showing in your table.

Efficiency is 96%

You forgot to mention that PowerWall 2 has a build in inverter/charger and this 90% is the round trip efficiency (AC to DC to AC).

So your table is not accurate.

0 Likes 0 ·
tgc avatar image
tgc answered ·

Hello! New to the forum, I just stumbled on the NiFe topic.

I have been living for 4 years with them now. Fully off-grid powering a large modern home entirely electric (HW, and cooking included). Off grid both by choice and... because in remote Australia you don't have a choice :)

So, summary of practical experience.

NiFe here are not a lot more expensive that other chemistries. So that's not a huge factor.

They are meant to last longer but after 4 years... I just don't know, honestly. Give me another 6. At the time I bought them there were no source I coud find here so I bought them from China. Not sure if it makes a difference in quality and therefore longevity.

My objective in buying them was longevity, yes but also robustness. I didn't want to worry about undercharging or overcharging. Again, a bit early to tell, but they are still alive despite some heavy cycling, and two total discharges. (#!@#$#@ inverter not behaving).

Refilling with water to be honest is a PITA. It's only 1 or 2 hours of work every 2 or three months - so not really much in the scheme of things, but just another maintenance job you'd rather not have to do... cost is nothing though. about 30-40l every 2-3 months. Now my batteries are especially hard to refill (china?). For example the shell is not transparent so hard to see where the level is at. So wjhilst refilling is not a huge deal, they are NOT fire and forget.

Charger/inverter settings. BIG DEAL ! I overlooked this one at the start, but it's very important. LVCO should be able to be set as low as 30V. (for a 48V ssytem) The internal resistance means that voltage will drop scaringly even on a 50% state of charge. If you inverter decides to stop playing, that is very annoying, basically leaves you with a whole lot of capacity you cannot tap into. Max charging voltage is another important one - you need to go up to 66-67V to charge them at max speed (but then that's a lot of amps so the charger need to be able to handle it)

Self discharge is not really a problem for solar application, they don't stay idle long enough ...

Efficiency is not really a problem either, as one of the other answers say panels are cheap enough these days to design for it.

So if I had to buy them again, I probably would IF they prove to have the longevity they claim. But in hindsight: a) I'd be choosing chargers and inverters that allow me to take full advantage of them - and to be frank the brand I have is utterly cr*p for this and other reasons. b) I'd pick a design easier to refill with water

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

Thank you for this real life report on those cells.

As I suspected they are good choice for total off-grid use.

The longevity is probably no longer their best advantage because LTO cells are probably as good in this regard and they have other important advantages over NiFe.

Their greatest advantage is that they are "idiot proof" or a disaster proof.

Automatic water replenishing systems are possible.

There is a NiFe maker in Ukraine that sells such an option for their cells.

I have seen something about that also from China's manufacturer of NiFe cells.

0 Likes 0 ·