Setting up 3 phase/2 parallel system - fixed

Hi,

I am trying to set up 3 phase/2 parallel system based on 6 MP-II.

How to set the master and slave in each phase?

screen-shot-2021-03-26-at-102000-pm.png

3 phasemultiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi,

Have you completed the 3 phase and parallel theory and practical training in Victron Professional?

https://professional.victronenergy.com/online-training/

I would be interest to hear if you had and it was still unclear. I could then make some specific improvements based on the steps you think are missing.

Once you have confirmed which units are connected in parallel in master slave to each other, this is how the programming should look:

cleanshot-2021-03-27-at-132309.jpg


7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

Hi @Guy Stewart (Victron Community Manager),

Yes I did completed this training and even got the diploma :)

And Yes, after I moved my MP-II pairs to respected "phases" I got the screen to look like yours.

Your screenshot shows in the "System check" box as "OK, Setup not send to system yet!"

I hope, to finish the setup I have to send it IN.

So I did, and at the end I had, in the "System check" box, only green "OK".

vebus-ok.jpg

Before I moved them from the right to the phase "boxes", I renamed them to know which is which.

Now when I click on the phase boxes 1, 2 or 3 on the left, I can see, on the right, the units assigned to each phase.

vebus-l1.jpg

vebus-l2.jpg

vebus-l3.jpg

It is not the first time I use VE.Bus System configurator.

I used it first to set up a 3 phase/1 parallel system out of 2 MP-II and 1 EasySolar-II.

Everything went OK than and it worked for 6 moths.

Now I want to add additional MP-II to each phase in parallel because I was getting an overload warnings because a load was sometime over the one MP-II limit.

I even payed (in advance) the Victron installer to do this job, but he came in with new MP-IIs and some needed hardware, told me what to do and went his "Merry Way" to more important clients.

So I did all the rewiring and waited for him to return and set it all up.

He promised to be back in on last Tuesday morning.

Than, on Wednesday, he called that he will come Thursday or Friday.

"No show" or call so far.

To be fair, he did not specify which week or month this Thursday of Friday will be. :) (it is not funny)

So I am trying it myself, because in 2 days there will be no power from the grid for whole day due to some repairs.

So far I have all kinds of LED lights flashing on all MP-II (except ES-II because it has no LEDs).

I would have included a video of those LEDs flashing on each MP-II but this system is not accepting my "mov" files. They are quite entertaining.

Here what ES-II is showing in terms of errors.

error-17.jpg

overload.jpg

So, the questions are:

How to make one MP-II a master and the other Slave?

What the heck is this overload error when there is no load connected?

Best Regards,

Marek

0 Likes 0 ·
vebus-ok.jpg (108.1 KiB)
vebus-l1.jpg (88.9 KiB)
vebus-l2.jpg (88.9 KiB)
vebus-l3.jpg (84.5 KiB)
error-17.jpg (29.0 KiB)
overload.jpg (35.5 KiB)

You do not need to choose the master, that happens automatically. I am guessing the phase master missing error is a secondary consequence of the overload.

It’s most likely a wiring issue, but very hard to say where to even start looking.

The wiring for parallel 3 phase is complex, and I would post the diagram, and the photos as best as you can of all connection points to perhaps see where it has gone awry.

1 Like 1 ·
marekp avatar image marekp Guy Stewart (Victron Community Manager) ♦♦ commented ·

Hi @Guy Stewart (Victron Community Manager),

Found IT.

I used connectors for making a "Y" connections.

They had a short in them between channels.

As a result, AC-Out outputs on 3 inverters were shorted.

My bad for not testing them.

Thank you for pointing me towards the wiring problem.

Hope after fixing it the rest will go without problems.

Regards,

Marek

0 Likes 0 ·

Happy to hear, please take care.

0 Likes 0 ·
marekp avatar image marekp Guy Stewart (Victron Community Manager) ♦♦ commented ·

@Guy Stewart (Victron Community Manager)

Thank you.

An update.

All is connected and set up as a 3phase/2parallel.

Now on to the next step, the ESS assistant.

Best Regards,

Marek

0 Likes 0 ·
zain avatar image zain Guy Stewart (Victron Community Manager) ♦♦ commented ·
Hi, i was wondering if you could share the wiring diagram of the 2 parallel 3 phase system. i did arrive on some conclusion, but i wanted ti check if i was on the correct path.
0 Likes 0 ·
zain avatar image zain Guy Stewart (Victron Community Manager) ♦♦ commented ·

Could you post the diagram? It would be very helpful. I did complete the 3 phase and parallel theory and practical training in Victron Professional and even tried out practically both the systems. But i was having difficulty when i wanted to combine both the systems. I am a little confused in the AC wiring since now there are 3 masters and 3 slaves.

0 Likes 0 ·