Power Assist function on AC IN Quattro

Hi, Experts.

The picture shows the connection and functions. Will this work? Any HELP! Thanks

1.jpg

ESSpowerassist
1.jpg (1015.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Kuban_invertor

For power assist to work, you need to connect the loads to the output of the inverter. You can than set a maximum AC input limit.

This also works when using ESS, but the loads still need to be on the output.


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jwfrary avatar image jwfrary commented ·

And you can put a larger load. On than the output of the inverters assuming you don’t exceed the transfer contactor rating for the model you have.

You could use the AC 2 out on the Quattro to switch a contactor and disconnect your large loads when the input power goes out.

0 Likes 0 ·
kuban-invertor avatar image kuban-invertor commented ·

Thanks for the answer! I got a call from a Victron distributor from Moscow. Here is his answer: "Possible. Power Assist will work through its AC-IN. And for scheduled charging you need to use the Quattro Digital Input. Is there a reason not to trust the distributor?)

0 Likes 0 ·
jwfrary avatar image
jwfrary answered ·

Why is the capacity of the grid changing? Is it solar?

The power assist function kicks in over a certain pre set amperage but there are ways around that depending on the reason.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kuban-invertor avatar image kuban-invertor commented ·

Thanks for helping me! There will be no solar panels in this system. Only power peak compensation. I found the text in the instructions - https://www.victronenergy.com/media/pg/Energy_Storage_System/en/configuration.html#UUID-7435bdda-8f3f-81c2-a1a6-dc8f1c9b2f8f. Clause 4.2 (note) says the following -

Notes with regards to the Input current-limit and PowerAssist:

Input current-limiter setting - The configured limit is used as the threshold for AC current at the AC-in of the Multi / Quattro. Further notice that:

Loads in parallel with the Multi / Quattro are not taken into account: therefore, install all loads on the AC-out of the Multi or Quattro in systems that require AC Input Current limiter functionality. For example - systems with a small AC load connected.

The current limiter will be used for both directions of the current.

The PowerAssist setting in VEConfigure3 will be disabled and ignored when ESS is installed.

The Dynamic current limiter in VEConfigure3 will be disabled and ignored when ESS is installed.

If I understand correctly, the ESS assistant cancels the power assist function. I just need an ESS to charge batteries at a night time.

Perhaps I misunderstand this point? thank

0 Likes 0 ·
Show more comments
jwfrary avatar image
jwfrary answered ·

if the graph is power demanded then yes it’s how power assist works. Be sure your battery capacity is high enough to deal with the duration of the peaks

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kuban-invertor avatar image kuban-invertor commented ·
This is the power consumption graph. I wrote it conditionally. The load current can exceed the current of the inverters. Therefore, I only want to connect via AC IN. So that there is no overload. And the UPS function is not required.
0 Likes 0 ·
kuban-invertor avatar image
kuban-invertor answered ·

If the Quattro is not able (in the presence of EM-24 or ET-340) to support the load at peak times together with the grid via AC-IN, then I see only one solution - to double the number of Quattro in order to avoid overloading the internal relay of the inverters. I'm right?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

What is ESS training video

ESS Quick Installation Guide

ESS design and installation manual