State of Charge never gets reset - BMV700 with MPPT 75/15 and 110W Solar panel

Hi, Sorry if this is a common question, I'm very new to Solar and trying to learn. I'm very impressed with my Victron gear but there is 1 problem.

I watched the Victron video explaining to change the BMV settings and have done so however the SOC detection still doesn't seem to be working...hope someone can offer some advice.

Setup:

120Ah "Fusion" brand battery

110W Solar Panel

BMV 700

MPPT 75/15

0.8A load

VenusOS on a Pi 3B+ with 2 x USB to VE Direct cables

The battery seems to be charging fine, I can see bulk then absorption then float phases. Unfortunately the SOC never gets reset at all, it just gradually declines until it's zero.

I haven't changed anything on the MPPT, it's by default at Factory default "Gel Victron deep discharge 2".

The BMV I have these settings:

Battery Capacity: 120Ah (I changed this)

Charged voltage: 13.5V (I changed this)

Tail Current: 4% (default)

Charged Detection time: 3m (default)


I set the charged voltage at 13.5V because I can't find the battery stat for this on the manufacturer's details so I looked at the average figure during absorption phase, 13.8. Based on this I set charged voltage at 13.5, 0.3 below absorption rate per video instructions here:

https://www.youtube.com/watch?v=4ReljfO3k6M

I guess I must have misunderstood something, can anyone help?

Thank you.




BMV Battery MonitorSOC
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Is the BMV wired correctly?

If the SOC only goes down until 0% even if the MPPT is charging I guess that the (-) of the MPPT is connected directly to the battery instead of to the "load/charger" side of the shunt.

13 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Dominic avatar image Dominic commented ·

Thank you, I agree the cabling doesn't look correct that my friend did. This diagram looks right and will be easier for us to follow. Would you mind checking it is correct please?

solar-panel-install-1-panelmpptbattery-monitor-pdf.jpg

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ Dominic commented ·

All loads and charger negatives must go on the "Loads/Charger" side of the shunt. You watched the video?

shunt.png

0 Likes 0 ·
shunt.png (140.6 KiB)
Show more comments
Dominic avatar image
Dominic answered ·

Photo of the install

20210213-092243.jpg


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

Well, that is a new way to mess up the shunt's wiring. A star for effort.

BMV quick install guide.

0 Likes 0 ·
Dominic avatar image Dominic klim8skeptic ♦ commented ·

Yes, I reviewed the cabling guide, he's cabled it wrong by the looks of it.

This video was also useful

https://youtu.be/MRljOaTdc3s


0 Likes 0 ·
Dominic avatar image
Dominic answered ·

These are the graphs from VRM portal