Smart mppt 150/35 gives error 33 allready at 130V. How can i change the setting to 150V?

Smartsolar MPPT 150/35 will not charge because it always gives error 33.

I have 2s2p config of 4 Panasonic HIT panels.

Voc is 133V. This is a lot less then the max. 150V

MPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
seb71 avatar image
seb71 answered ·

When cold, the actual voltage can be higher than VOC from PV panel specifications.

Did you actually measured it and it was 133V or it's the value from PV panel specifications (for the string of panels)?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rene-e700 avatar image rene-e700 commented ·

It is the measured value in the App.

screenshot-20210220-114511.jpg

0 Likes 0 ·
seb71 avatar image
seb71 answered ·

Maybe there are short duration voltage spikes up to 150V.

Try to monitor it for a while, using the "Trends" tab (and select "Solar Voltage").


Would not hurt to also actually measure the voltage at MPPT's PV terminals, with a multimeter.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rene-e700 avatar image rene-e700 commented ·

The problem is continuously and i see no spikes.

If it is not possible to change the setting then i believe it is a wrong factory setting or a bug.

Thnx for your response.

0 Likes 0 ·
seb71 avatar image seb71 rene-e700 commented ·

More likely a defective unit.


Is it new?

0 Likes 0 ·
rene-e700 avatar image rene-e700 seb71 commented ·

Yes it is brandnew

0 Likes 0 ·
seb71 avatar image seb71 rene-e700 commented ·

Contact the seller.

0 Likes 0 ·
rene-e700 avatar image rene-e700 seb71 commented ·

I will. thnx.

0 Likes 0 ·
veganbiker avatar image
veganbiker answered ·

I am experiencing the same thing with both of my 150/35 bluesolar controllers. They both came from Amazon, 2 different arrays, a Canadian solar 2S2P:
https://www.altestore.com/static/datafiles/Others/CanadianSolar-HiKu_CS3W-MS_430-455_Datasheet.pdf

Datasheet max Voc: 97.8v

and a 3S2P Grape solar array
https://www.altestore.com/static/datafiles/Others/CanadianSolar-HiKu_CS3W-MS_430-455_Datasheet.pdf

Datasheet max Voc: 121.35v

Neither of these should be able to get to 150v, while I was looking at the logs on VRM I saw these random spikes, where exactly could they be coming from? even still they are lower than 150V

screenshot-from-2022-02-20-15-04-58.pngscreenshot-from-2022-02-20-15-04-45.png


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image JohnC ♦ commented ·
@VeganBiker

Spikes like this can often be associated with the mppt tracking. It's a bit of a coincidence that vrm picks it up, but on VictronConnect Trends, the per-second logging will usually show this clearly, with multiple scans over a few seconds. Every 10 minutes, if the mppt is under target V.

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ commented ·
@VeganBiker

Also temperature. The panels are rated at 25°C, so colder they produce more.

0 Likes 0 ·
kevgermany avatar image
kevgermany answered ·

The spikes could be higher that the graph due to averaging between the reporting points.

Hope the others have better ideas, but check the wiring carefully for loose/poor connections, and possible shorts from another source. Are the panels properly grounded, could they be getting external voltage input?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.