Multiplus 2 fluctuations


Hello, Since the installation almost a year ago I have had problems with strong fluctuations on phase 1, where the PV inverter and Multiplus 2 are also connected.

These fluctuations can go up to several hundred watts for a short time. The fluctuations are also present at night, but not as strong.

No loads are connected to phase 1, but loads are displayed and actually consumed.

In the meantime I have separated all loads on AC-out1 and AC-out2 for testing. This brought no change.

The system is installed in Austria, the configuration for Austria programmed in Multiplus 2.


Here is a short video where you can see the fluctuations on L1 under AC loads:



I have no more idea why that could be. I would be very grateful for your help.

BR
chris



System is running in ESS optimized mode without battery life, no scheduled charging.

1xMultiplus-II 3000
Venus GX
EM24
3x Pylontech US2000 7,2 kWh
AC coupled PV-Inverter Fronius Primo 4.0 connected to AC-in


Multiplus-II
unbenannt-4.mp4 (1011.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Paul B avatar image
Paul B answered ·

have a look at the mutliphase regulation and read up on this. as this maybe you issue. its used to try and balance the phases, you can turn it off


1612003152503.png


1612003152503.png (27.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chris2 avatar image
chris2 answered ·

Hi, thanks for your answer.

That´s not the issue. I need to set it to "total of all phases".

Even setting it to single phase there is no difference. Fluctuations up to several hundred watts.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chris2 avatar image
chris2 answered ·



Look at that strong fluctuations at L1 under "AC Lasten" . There must be something wrong. Normally it should be 0 watts since there is nothing connected !


unbenannt-6.mp4 (1.6 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image
seb71 answered ·

Is your system supposed to inject (feed in) power into the grid or not?

What is your "Grid setpoint" if not?

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chris2 avatar image chris2 commented ·

System is allowed to feed in.

0 Likes 0 ·
seb71 avatar image seb71 chris2 commented ·

Then what's the problem? It is feeding in.

0 Likes 0 ·
chris2 avatar image chris2 seb71 commented ·

Look at "AC Lasten" L1. There is nothing connected to L1. It has nothing to do with feed in. It seems there are loads connected to L1.