Multiplus 2 Overloads and Randoms Shuts Down...Grid connection problems

All those experiencing the same problems outlined abive..i encourage you to check out firmware version 478 for the MP2. Been a week now and have numerous loadshedding sessions....the system has been very stable.


I struggled with these tripping nuesances and want to let everybody know that the MP2 is doing in well especially with our weak grid here in Zimbabwe

Multiplus-II
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Rob Duthie avatar image Rob Duthie commented ·

Hi

Yes i the same issue with spurious shut downs on low loads of 1 to 2.5 kw on a 2x 5kw multiplus2 in parallel. I did the version 478 upgrade problem not fixed still does random shut downs?

Rob D

NZ

0 Likes 0 ·
reed avatar image reed Rob Duthie commented ·

Are you using a bms controllee battery? Are yo getting any errors causing the battery to be opening and closing its contactors?

Have you tried to UP the low voltage Ac shut down? I would try to set it at plus 200Ac and 205 reconnection.

Also what grid code are you using?

0 Likes 0 ·