I have a Multiplus 24/5000 with a CCGX. Both the Multiplus and CCGX have an input current limit at 10 A (around 2300W). When the AC input is active the current goes way above the 10 A.
Any ideas?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have a Multiplus 24/5000 with a CCGX. Both the Multiplus and CCGX have an input current limit at 10 A (around 2300W). When the AC input is active the current goes way above the 10 A.
Any ideas?
Ok. I contacted my supplier (ARESTIPOWER) and he recommended enabling the power assist. I already tried it and it keeps the incoming AC power low! It is a good solution. Thank you
Ahh super!
I should have thought to suggest that first!
Success!
For some reason your system is in Passthru mode - please read ESS FAQ #4 for info on how to correct this.
Hello! My system is not ESS. It is a AC coupled system using the AC input with the help of the GENERATOR START STOP settings. The CCGX triggers a relay that connects the grid on the AC input with an external realy. All the parameters described on the FAQ #4 do not apply to my system. What else can it be?