question

granvillea avatar image
granvillea asked

MPPT to inverter without batteries

Hi everybody,

I'm currently searching for a way to power a load of 5A/230V with a few solar panel. According to my calculations, I should buy 4 solar panel of 360Wp, to power the 1150W needed. I want those solar panel to be connected to a MPPT and an inverter without any batteries between those two. The installation is completely PLC-controled and I want to power my load only when the sun shines. I will have a contactor to connect my load and my solar panel together.

Is it possible to connect my solar panels to an MPPT and in an inverter without batteries between ? I' do not have any acces to the electrical-grid.

Thanks for reading me,

Granville. A.


MPPT SmartSolarPhoenix Inverterbattery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

Hi @GranvilleA

It is possible but will not always be stable, it also depends on the loads you are running. Most inverters and mppts use the batteries as a reference for production and voltage stability. You are also assuming the solar panels will always out put the power you are looking for, in real world application this is not always the case.

Depending on the loads you would like to start up as well you would need some ability for surge draw, like a motor start up and would also need to wait until you are in peak production to run your proposed load, with plc I guess this is not an issue but it would shorten your day runtime.

The next consideration is that you are not using the equipment as recommended by manufacturer so most likely will be voiding warranty. That being said there are several threads on this community with similar thoughts as yours

https://community.victronenergy.com/questions/26030/mppt-without-battery.html

https://www.victronenergy.com/live/drafts:mppt_faq#q4can_the_output_of_the_mppt_be_used_as_a_power_supply_thus_without_batteries
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.