Hi folks,
I cant get my battery to charge at more than about 2kW and I cant see why... Obviously missing something?
Small genny, circa 5kW on AC1. AC current limit set to hold that at 19A, circa 4kW, and working. Gen is a recent upgrade, previous unit was smaller.
Putting a 2kW load on results in circa 1.5kW charge whilst running the load, genny a tad over 4kW.
Dynamic limit is off, Weak AC is on - hence the losses I assume.
Bat will not charge above 2kW and typically hovers at 2kW+/- 80W, which looks suspissiously like a limit of some sort.
Easy solar so Multypluss 48/5000/70.
BYD 13,8kW (Temp mainined at 15C min)
Clearly I am missing something and would apriciate somone pointing out what Iam doing wrong or failing to apriciate.
Cheers,
Al