Cerbo with 10 MPPTs losing connection

We have 2 sites with 3 phase 15000 Quattros, Cerbo, FreedomWon BMS battery and 10 smart mppts.

Both for some reason keeping having the MPPTs switch to float and back to remote control. The power then fluctuates wildly.

Both sites have the BMS on the same bus and I see many TX/RX can errors.

We originally tried to have the BMS on the BMS-CAN interface but it would not come up even though the same cable/bms worked on a Octo.

The 1 site BMS does not auto sense the baud rate but the other does, so we will arrange to move the cable to see if it resolves the problem. If that works we will reprogram the other BMS to 500kbs and try again.

Can you confirm this is definitely the issue as both sites are not that accessible.

MPPT SmartSolar
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

hardwic avatar image hardwic commented ·

We can confirm moving the 1 BMS onto a separate CAN bus does not solve the problem. Bellow the MPPT state and resulting yield.

0 Likes 0 ·
1 Answer
hardwic avatar image
hardwic answered ·

I must just add that most the issues here seem to relate to CAN cable being run in conduit with DC power conductors. Varying DC loads could result in magnetic interference in adjacent comms cables. We have now corrected this and are monitoring.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

michelg avatar image michelg commented ·

Hi Hardwic ! I had such kind of issues with the ET112 and RS485 wiring, even using the Victron cable. By moving it only a few centimeters did solve my issue.

You are probably the right way. Interferences are a nightmare to detect and fix. Good luck.