We have 2 sites with 3 phase 15000 Quattros, Cerbo, FreedomWon BMS battery and 10 smart mppts.
Both for some reason keeping having the MPPTs switch to float and back to remote control. The power then fluctuates wildly.
Both sites have the BMS on the same bus and I see many TX/RX can errors.
We originally tried to have the BMS on the BMS-CAN interface but it would not come up even though the same cable/bms worked on a Octo.
The 1 site BMS does not auto sense the baud rate but the other does, so we will arrange to move the cable to see if it resolves the problem. If that works we will reprogram the other BMS to 500kbs and try again.
Can you confirm this is definitely the issue as both sites are not that accessible.