Quatro 10kva inverter charger with 7.5kva Generator

Quatro 10kva inverter charger with 7.5kva Generator want to start generator manually through A/C 2 in on inverter are there any implications to doing this ?

victron community
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@Marc

AC2 is the usual input for the generator unless you are offgrid. If you have a GX device make sure it is assigned that way.

The only 'surprise' we had was from dead battery (black start) we could not recover/wake up the system through AC2 charging with the generator. It does from AC1.

Using AC2 in is great though as there are quite a few assistants that can be programmed for the generator. Manual start is also fine.

0 Likes 0 ·
jacobjned avatar image jacobjned Alexandra ♦ commented ·

Would also like to add in case you haven't done so, that you will have to alter ac input current within the Genset current limits. Enable Dynamic Current limiter and probably AC Weak grid.

0 Likes 0 ·
petajoule avatar image petajoule jacobjned commented ·

Except we're currently unable to confirm that dynamic current limiter actually works:

https://community.victronenergy.com/answers/64591/view.html

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ petajoule commented ·

Dynamic Current Limiter does not work in an ESS system, but in other systems (off-grid usually) it does work. Note that it is really meant for small inverter-type (variable speed) generators.


About ESS:

As is written in the manual, and stated when you configure the ESS assistant:

https://www.victronenergy.com/live/ess:design-installation-manual#multi_quattro_and_ess_assistant

0 Likes 0 ·
petajoule avatar image petajoule Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

Said system is not an ESS and there is no ESS assistant installed.

The generator is not a small inverter type, but it is small enough to not be able to provide the loads the quattros can cope with - and are designed for.