Quatro 10kva inverter charger with 7.5kva Generator want to start generator manually through A/C 2 in on inverter are there any implications to doing this ?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Quatro 10kva inverter charger with 7.5kva Generator want to start generator manually through A/C 2 in on inverter are there any implications to doing this ?
@Marc
AC2 is the usual input for the generator unless you are offgrid. If you have a GX device make sure it is assigned that way.
The only 'surprise' we had was from dead battery (black start) we could not recover/wake up the system through AC2 charging with the generator. It does from AC1.
Using AC2 in is great though as there are quite a few assistants that can be programmed for the generator. Manual start is also fine.