Quatro 10kva inverter charger with 7.5kva Generator

Quatro 10kva inverter charger with 7.5kva Generator want to start generator manually through A/C 2 in on inverter are there any implications to doing this ?

victron community
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@Marc

AC2 is the usual input for the generator unless you are offgrid. If you have a GX device make sure it is assigned that way.

The only 'surprise' we had was from dead battery (black start) we could not recover/wake up the system through AC2 charging with the generator. It does from AC1.

Using AC2 in is great though as there are quite a few assistants that can be programmed for the generator. Manual start is also fine.