Quatro 10kva inverter charger with 7.5kva Generator

Quatro 10kva inverter charger with 7.5kva Generator want to start generator manually through A/C 2 in on inverter are there any implications to doing this ?

victron community
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@Marc

AC2 is the usual input for the generator unless you are offgrid. If you have a GX device make sure it is assigned that way.

The only 'surprise' we had was from dead battery (black start) we could not recover/wake up the system through AC2 charging with the generator. It does from AC1.

Using AC2 in is great though as there are quite a few assistants that can be programmed for the generator. Manual start is also fine.

0 Likes 0 ·
jacobjned avatar image jacobjned Alexandra ♦ commented ·

Would also like to add in case you haven't done so, that you will have to alter ac input current within the Genset current limits. Enable Dynamic Current limiter and probably AC Weak grid.

0 Likes 0 ·
petajoule avatar image petajoule jacobjned commented ·

Except we're currently unable to confirm that dynamic current limiter actually works:

https://community.victronenergy.com/answers/64591/view.html

0 Likes 0 ·