question

mhuusko avatar image
mhuusko asked

Initial charging of smart litium with agm charger

can initial charging of smart litium be done with standard agm charger.

battery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Mhuusko

Please follow the manual on this. you could use any charger that puts out the correct voltage...as long as it is controlled by the BMS!!

'a AGM charger' doesn't say anything.


ps. if it's a 12V system than you don't have to do an initial charge, only when you put multiple batteries in series.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mhuusko avatar image mhuusko commented ·

I’m about to in parallel connect an additional 200 Ah battery to my RV.

The new battery cell are at 3.26V.

Only hava a Ctek MSX 25 external charger, could it be used?

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ mhuusko commented ·

@Mhuusko

again: for a parallel connected battery you don't need an initial charge, just make sure they are both at about the same voltage before connecting.

in your system, make sure the BMS controls the charging / discharging as in the manuals.

0 Likes 0 ·
Show more comments