Settings Depth of discharge offgrid

Hi

My setup:

Multiplus 2 5000

Byd b box pro 13.8

Im searching for the settings for depth of discharge setting. I can only find it at ESS but its not allowed to activate it running an offgrid version

I would like to shut down the system at 15% and reactivate the inverter at 18%.

Thanks it andance

BMV Battery Monitorbattery capacity
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@Melonentier

You can set it using ve config on the inverter tab. Check shutdown on low SOC and set your percentage there. You will need to enable battery monitor on the general tab first.

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

melonentier avatar image melonentier commented ·

Thanks for you answer.

I activated the battery monitor at the general tap and entered the capacity.

At the inverter tap i can only find

DC imput loq shutdown 37.20volt

Dc imput low restart 43.6volt

Dc imput low pre alarm 43.6volt


Im searching for the settings at % of battery depth of discharge.

0 Likes 0 ·
intra avatar image intra melonentier commented ·

I thought that when you use the ESS assistant it ignores the inverter tab shutdown values.


https://www.victronenergy.com/live/ess:design-installation-manual

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ intra commented ·

It is not recommended to use ESS in an offgrid setup.

@Melonentier you may need to update ve config then, this is the version i am running.

0 Likes 0 ·
1596726038191.png (14.7 KiB)
1596726103516.png (22.8 KiB)
melonentier avatar image melonentier Alexandra ♦ commented ·

Hello alexandra.

Im running the same version but i cant see the shut down at soc...

90.04.220

Is there any seting need to be done to see it except the battery monitor?

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ melonentier commented ·

@Melonentier

I have no idea on that. Sorry.

0 Likes 0 ·
Show more comments
Alexandra avatar image Alexandra ♦ melonentier commented ·

@Melonentier

Another thought here is the firmware on your inverter up to the latest release?

0 Likes 0 ·
melonentier avatar image
melonentier answered ·

I updated the firmare of the multiplus via mk3 and victronconnect to 470. After this the setting popped up to edit. The update resets all the settings make sure to save it first.

Thanks fpr your help!